Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the setting of the branch circuits(Wye of Delta) of HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: Regarding the setting of the branch circuits(Wye of Delta) of HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-09-25 02:00 AM

1 Like
6
339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-25 02:00 AM

Regarding the setting of the branch circuits(Wye of Delta) of HDPM6000

Hello,

 

I have a question about the branch circuit settings for the HDPM6000.
In the Channel Config tab, when combining three circuits, you can choose whether the branch circuit is Wye or Delta. How does this setting affect measurements and other values?
In my environment, I applied voltage and current using a tester with both options, and they appeared to show the same values. I couldn’t see any difference, so I’m asking for clarification.

Regards,

Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-25 11:02 AM

1 Like
4
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-25 11:02 AM

Hi @T.Okada 

 

Yes, as long as the physical installation is wired properly for the system type and the matching option (Wye or Delta) is selected in the Channel Cfg tab, the meter will calculate true aggregate 3-phase power (kW, kVAR, kVA, and Power Factor) accurately.

 

Mehran_Mehrnia_0-1790358586818.png

 

Individual Channel Measurements:
Single-channel parameters (such as raw branch current or phase voltage) do not change because the physical CTs measure current directly regardless of topology. This is why basic individual tester inputs look identical in both modes.

 

3-Phase Aggregate Power Calculations:

The Wye vs. Delta toggle changes the internal math used to calculate total 3-phase power across the combined channels:

 

  • Wye Configuration: Calculations reference Line-to-Neutral (VL-N) voltages across all 3 phases (3-element measurement).

  • Delta Configuration: Because a standard 3-wire Delta system has no neutral wire, the meter uses Blondel’s Two-Wattmeter Method using Line-to-Line (VL-L) voltages.

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-09-28 08:22 AM

1 Like
1
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:22 AM

Hello @T.Okada ,

 

For example you could have a head unit connected to a wye system, 80% of the circuits in the panel are connected wye, 20% of the circuits in the panel are connected Delta. You would wire the head unit as wye and configure circuits based on what the wiring in the panel is.

However if head unit is delta, then will not be able to monitor any circuits in the panel as wye.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 6
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-25 11:02 AM

1 Like
4
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-25 11:02 AM

Hi @T.Okada 

 

Yes, as long as the physical installation is wired properly for the system type and the matching option (Wye or Delta) is selected in the Channel Cfg tab, the meter will calculate true aggregate 3-phase power (kW, kVAR, kVA, and Power Factor) accurately.

 

Mehran_Mehrnia_0-1790358586818.png

 

Individual Channel Measurements:
Single-channel parameters (such as raw branch current or phase voltage) do not change because the physical CTs measure current directly regardless of topology. This is why basic individual tester inputs look identical in both modes.

 

3-Phase Aggregate Power Calculations:

The Wye vs. Delta toggle changes the internal math used to calculate total 3-phase power across the combined channels:

 

  • Wye Configuration: Calculations reference Line-to-Neutral (VL-N) voltages across all 3 phases (3-element measurement).

  • Delta Configuration: Because a standard 3-wire Delta system has no neutral wire, the meter uses Blondel’s Two-Wattmeter Method using Line-to-Line (VL-L) voltages.

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-09-28 12:41 AM

1 Like
3
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 12:41 AM

Hi @Mehran_Mehrnia,

 

Thank you for your reply.

 

As a criterion for choosing Delta or Wye when combining three branch circuits, should we decide based on whether the main feeder is three-phase four-wire or three-phase three-wire?

 

Regards,

Okada

 

 

Reply
AnandSingh
AnandSingh Mentor
Mentor

Posted: ‎2026-09-28 02:01 AM

1 Like
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 02:01 AM

Hi  
T.Okada

Not necessarily. Choose Wye or Delta based on the electrical system connected to the HDPM6000, not just the main feeder.
Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-28 08:18 AM

0 Likes
0
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:18 AM

Hi @T.Okada 

 

The selection criterion for combining channels as Wye or Delta in the Channel Config tab should strictly match the physical wiring topology of the circuit being measured and connected to the HDPM6000:

Wye (3-Phase 4-Wire): Select this if the physical circuit includes a Neutral conductor connected to the meter's reference terminal.

Delta (3-Phase 3-Wire): Select this if it is a 3-wire line with no Neutral reference connected to the meter.

 

Additional Consideration:
If the main feeder carries a Neutral because it serves single-phase or unbalanced loads, you must connect the Neutral wire to the HDPM6000 and select Wye to ensure accurate 3-phase power and energy calculations. Omitting the Neutral wire and configuring as Delta is only valid if the downstream load is strictly a 3-wire, 3-phase balanced load (such as a 3-phase motor).

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-09-28 08:22 AM

1 Like
1
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:22 AM

Hello @T.Okada ,

 

For example you could have a head unit connected to a wye system, 80% of the circuits in the panel are connected wye, 20% of the circuits in the panel are connected Delta. You would wire the head unit as wye and configure circuits based on what the wiring in the panel is.

However if head unit is delta, then will not be able to monitor any circuits in the panel as wye.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-10-04 11:16 PM

0 Likes
0
247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-04 11:16 PM

Hello @AnandSingh , @Charles_Murison , @Mehran_Mehrnia 

 

Thank you for your reply.


I understand that the choice between Wye and Delta affects how power is calculated.

Regards,

Okada

 

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore