Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the "Phase V watchdog" settings of the HDPM6000 web interface

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the "Phase V watchdog" settings of the HDPM6000 web interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
573
Mehran_Mehrnia
Mehran_Mehrnia Champion
210
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-25 01:47 AM

0 Likes
8
392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-25 01:47 AM

Regarding the "Phase V watchdog" settings of the HDPM6000 web interface

Hello,

 

I have a question about the "Phase V Watchdog" setting in the HDPM6000 web interface.
At our customer’s site, voltage measurement is not used.
When the "Phase V Watchdog" is enabled under this condition, the HDPM6000 reboots every minute, which appears to cause instability.

To prevent this, we would like to disable the "Phase V Watchdog."
Could you advise on the impact or potential risks of disabling this feature?
If there are recommended settings or best practices for systems without voltage measurement, please let us know.

 

Regards,
Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-28 08:51 AM

0 Likes
0
286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-28 08:51 AM

Hi @T.Okada 

 

Your understanding is reasonable. If there is intentionally no voltage connected to the HDPM6000, a restart by itself will not restore the missing voltage. Therefore, in that situation, the Phase V Watchdog is not expected to change the measurement result, since the voltage source is still absent.

The intent of the Phase V Watchdog is generally to provide a recovery mechanism for situations where voltage is expected to be present but the system encounters an unexpected condition that results in the loss of a valid voltage reference. In those cases, the watchdog attempts to recover normal operation automatically.

 

In our testing, with the Phase V Watchdog enabled and no voltage connected to the head unit voltage inputs, we observed that the device periodically entered a recovery cycle. During this process:

  • Voltage measurements remained at 0 V.
  • Current measurements briefly dropped to 0 A.
  • Diagnostic messages such as PT wiring or phase setting errors appeared.
  • The display then returned to normal operation.
Mehran_Mehrnia_0-1787932108911.png


However, because no voltage source was actually present, the recovery cycle did not restore a voltage measurement. This is consistent with your observation that a restart cannot create a voltage signal that is physically absent.

 

If your application does not use voltage measurements, and the voltage inputs are intentionally left disconnected, then leaving the Phase V Watchdog disabled would generally be a reasonable approach. Doing so would also avoid the periodic recovery cycles that occur when the watchdog continuously detects the absence of voltage.

 

Based on our testing, we are not aware of any adverse impact to current-only monitoring caused by disabling the Phase V Watchdog when voltage inputs are intentionally unused. The primary consequence is simply that the watchdog will no longer attempt to recover from a missing voltage condition.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 8
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-08-25 11:36 AM

0 Likes
1
377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-25 11:36 AM

Hello @T.Okada ,

 

In the Head unit install guide there is a line on page 22

"Disable the voltage watchdog in the General Settings tab if the meter voltage inputs are zero, during commissioning or maintenance."

 

The watchdog is doing exactly what it was designed to do. Reboot the meter if voltage readings are zero.

given you know that no voltages are being used I would recommend disabling the watchdog.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-25 11:37 AM

0 Likes
1
377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-25 11:37 AM

Hi @T.Okada 

 

The Phase V Watchdog is designed to monitor the voltage reference inputs (P1, P2, P3, N). When enabled, the watchdog will reboot the meter every minute if no voltage is detected on the voltage inputs.

The HDPM6000 is a power meter and designed to operate with three key connections:

  1. Voltage reference inputs
  2. Power supply
  3. CT inputs

The installation guide states that all three components are required for normal system operation. The voltage reference is used for many core metering functions, including voltage, power, energy, power factor, frequency, voltage alarms, power quality measurements, and waveform capture functions.

For applications where no voltage reference is intentionally connected, leaving the Phase V Watchdog enabled will result in the behavior you are observing, namely a periodic reboot every minute due to the absence of detected voltage. The guide specifically instructs users to disable the voltage watchdog when voltage inputs are zero during commissioning, maintenance, or firmware upgrade activities.

If the watchdog is disabled:

  • The HDPM6000 will no longer reboot when voltage is absent.
  • The meter will not automatically detect and recover from voltage-reference-related issues such as:
    • Loss of source voltage
    • Blown voltage fuse or breaker
    • PT secondary failure
    • Disconnected voltage wiring
    • Voltage reference wiring faults
  • Any measurements or functions requiring voltage inputs will remain unavailable or invalid.

Therefore, if the application is intentionally configured without voltage measurement, disabling the Phase V Watchdog is the practical recommendation to prevent unnecessary reboots. However, this is outside the normal metering configuration described in the installation guide, and the customer should be aware that voltage-dependent measurements and power quality functions will not be available.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-26 02:51 AM

0 Likes
0
349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-26 02:51 AM

Hi @Mehran_Mehrnia,


Thank you for your reply!

 

There is one thing I don’t fully understand.

I understand that the V watchdog operates when there is no voltage,

but even if the meter restarts as a result, the input voltage to the voltage measurement remains at 0.

Therefore, I don’t think measurements that rely on voltage can function properly after a restart, and I’m not sure what the benefit is. Do you know the reason?

As a non‑expert idea, if we have to toggle the V watchdog on and off for maintenance or updates,

it seems like leaving it off from the start wouldn’t make much difference.

In fact, I’m concerned that repeated restarts while the voltage is zero could affect the current measurements that are functioning and the communications with the central monitoring system,

which makes it feel like there are only disadvantages.

If turning off the V watchdog has a significant impact on the system,

I’m willing to keep it on; however, if there aren’t major downsides,

would it be acceptable to leave it off even in a system that performs voltage measurements?

 

One more clarification: regarding the watchdog, does the “restart” mean a software reboot inside the meter rather than a complete power-off of the control power supply?

 

Regards,

Okada

 

 

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-26 03:12 AM

0 Likes
0
349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-26 03:12 AM

Hi @Charles_Murison,

 

Thank you for your response.

As you mentioned, if our customer does not need voltage measurements, we will disable the V watchdog.

By the way, starting from firmware version v0.66.0, we can display the current value even without a voltage input. In this case, if the customer does not need voltage measurements, is it acceptable to leave the voltage terminals unconnected?

 

Regards,
Okada

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-26 08:35 AM . Last Modified: ‎2026-08-26 08:38 AM

1 Like
1
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-26 08:35 AM

Hi @T.Okada 

 

The Phase V Watchdog is primarily intended to detect and recover from an unexpected loss of voltage reference in installations where voltage should normally be present. If the system is intentionally operated without voltage inputs, the watchdog cannot restore voltage-dependent measurements, so disabling it is typically the preferred approach to prevent continuous reboots.

The restart is an internal meter reboot, not a removal of external control power. For installations that use voltage measurement normally, it is generally recommended leaving the watchdog enabled.

Yes. Starting with HDPM6000 firmware v66.0, the behavior where current was reported as zero when the corresponding voltage input was zero was corrected. As a result, current measurements can now be displayed even when voltage inputs are not connected.


Therefore, if the customer's application only requires current monitoring and does not require voltage or other voltage-dependent measurements, it is acceptable to leave the voltage terminals unconnected. In this case, disabling the Phase V Watchdog is also recommended to prevent unnecessary reboots caused by the intentional absence of voltage inputs.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-27 05:46 PM

0 Likes
0
315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-27 05:46 PM

Hi @Mehran_Mehrnia ,

 

Thank you for your reply.

I understand about the "Phase V watchdog" settings under the system without using voltage measurements.

but I still don’t fully understand the intent of the statement that the Phase V Watchdog is designed to detect and recover from an unexpected loss of voltage reference in installations where voltage should normally be present. Even if the HDPM restarts after detecting an unexpected loss, I don’t see how that would change the fact that the measured voltage is still missing, so I’m not sure what the restart is meant to accomplish.

If I can’t understand that point, it seems cumbersome to toggle the setting on and off during maintenance when no voltage is applied, so I’m inclined to think there’s no particular need to keep it enabled. Would that be acceptable? Or could leaving it disabled cause any issues?

 

Regards,

Okada

 

 

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-28 08:51 AM

0 Likes
0
287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-28 08:51 AM

Hi @T.Okada 

 

Your understanding is reasonable. If there is intentionally no voltage connected to the HDPM6000, a restart by itself will not restore the missing voltage. Therefore, in that situation, the Phase V Watchdog is not expected to change the measurement result, since the voltage source is still absent.

The intent of the Phase V Watchdog is generally to provide a recovery mechanism for situations where voltage is expected to be present but the system encounters an unexpected condition that results in the loss of a valid voltage reference. In those cases, the watchdog attempts to recover normal operation automatically.

 

In our testing, with the Phase V Watchdog enabled and no voltage connected to the head unit voltage inputs, we observed that the device periodically entered a recovery cycle. During this process:

  • Voltage measurements remained at 0 V.
  • Current measurements briefly dropped to 0 A.
  • Diagnostic messages such as PT wiring or phase setting errors appeared.
  • The display then returned to normal operation.
Mehran_Mehrnia_0-1787932108911.png


However, because no voltage source was actually present, the recovery cycle did not restore a voltage measurement. This is consistent with your observation that a restart cannot create a voltage signal that is physically absent.

 

If your application does not use voltage measurements, and the voltage inputs are intentionally left disconnected, then leaving the Phase V Watchdog disabled would generally be a reasonable approach. Doing so would also avoid the periodic recovery cycles that occur when the watchdog continuously detects the absence of voltage.

 

Based on our testing, we are not aware of any adverse impact to current-only monitoring caused by disabling the Phase V Watchdog when voltage inputs are intentionally unused. The primary consequence is simply that the watchdog will no longer attempt to recover from a missing voltage condition.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-09-04 12:44 AM

0 Likes
0
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-04 12:44 AM

 

Hello @Mehran_Mehrnia 


Thank you for your reply.
I understand that the "Phase V watchdog" setting is intended to prevent the head unit from malfunctioning.

 

Regards,
Okada

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore