Hi,
I noticed a mismatch between the iTHD (%) description in the HDPM6000 protocol guide and the measured values.
The protocol guide states the following:
I compared the Modbus iTHD (%) values for the branch circuits with the values shown on the HDPM6000 web interface. If the description above is correct, the web values should be 0.41%, 0.31%, and 0.27%, but the web interface shows 4.1%, 3.1%, and 2.7%.
Is this an error in the manual, or are the web interface values incorrect?
Regards,
Okada
Link copied. Please paste this link to share this article on your social media post.
Hi @T.Okada
The web interface is correct. The manual’s statement that harmonic distortion values are expressed in units of 0.1% is also correct.
However, the example shown in the manual places the decimal point incorrectly. A value of 27 in the Modbus register should be interpreted as 2.7%, and this same value will be displayed as 2.7% in the web interface.
Therefore, the values shown on the webpage (4.1%, 3.1%, and 2.7%) are correctly correlated with the values returned via Modbus (41, 31, and 27), which are divided by 10 and expressed as percentages.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @T.Okada
The web interface is correct. The manual’s statement that harmonic distortion values are expressed in units of 0.1% is also correct.
However, the example shown in the manual places the decimal point incorrectly. A value of 27 in the Modbus register should be interpreted as 2.7%, and this same value will be displayed as 2.7% in the web interface.
Therefore, the values shown on the webpage (4.1%, 3.1%, and 2.7%) are correctly correlated with the values returned via Modbus (41, 31, and 27), which are divided by 10 and expressed as percentages.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Thank you for your kind reply.
I now understand the iTHD value of the HDPM6000.
Regards,
Okada