Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the Waveform format of HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the Waveform format of HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-04-24 12:08 AM

0 Likes
4
997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-24 12:08 AM

Regarding the Waveform format of HDPM6000

 

Hi,

 

I captured CSV waveform data from the HDPM6000 Head Unit and the HDPM6000R retrofit unit

(with voltage and current at 60 Hz).

I counted a total of 2048 samples in each waveform.

The data appears to be formatted as 128 samples per cycle over 16 cycles. Is this correct?

Is the same format used in a 50 Hz environment?

Also, can the waveform format be changed?

For example, 64 samples × 32 cycles.

I would like to know the waveform trigger point used by the HDPM6000.

 

Thank you,
Okada

 

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-24 08:38 AM . Last Modified: ‎2026-04-24 08:43 AM

1 Like
1
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-24 08:38 AM

Hi @T.Okada 

 

Based on Table 3.1 – Waveform Capture Specifications in the HDPM6000 Installation Guide:

Mehran_Mehrnia_0-1777042401265.png

HDPM6000 uses a fixed sampling frequency of 8 kHz means sample interval = 125 µs for its waveform captures, regardless of the line frequency.

For 60 Hz: each cycle is 1/60 ≈ 16.66 ms therefore each cycle includes (16.66 ms)/(125 µs) ≈ 133.33 samples

For 50 Hz: each cycle is 1/50 = 20 ms therefore each cycle includes (20 ms)/(125 µs) = 160 samples

 

The HDPM6000 waveform capture uses a fixed buffer length of total 2048 samples per waveform, regardless of frequency or module type.

At 60 Hz, 2048 samples at 133.33 samples/cycle equals 15.36 cycles. -> sampling × cycles = 133.33 × 15.36

At 50 Hz, 2048 samples at 160 samples/cycle equals 12.8 cycles. -> sampling × cycles = 160 × 12.8

 

The waveform capture format of is a fixed and cannot be changed.

 

Trigger is event‑based, with 2/3 pre‑event, and waveforms are captured when:

Voltage swell or sag crosses an RMS threshold
Overcurrent or tripped breaker conditions occur
A manual “Force Capture” is issued

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 4
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-24 08:38 AM . Last Modified: ‎2026-04-24 08:43 AM

1 Like
1
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-24 08:38 AM

Hi @T.Okada 

 

Based on Table 3.1 – Waveform Capture Specifications in the HDPM6000 Installation Guide:

Mehran_Mehrnia_0-1777042401265.png

HDPM6000 uses a fixed sampling frequency of 8 kHz means sample interval = 125 µs for its waveform captures, regardless of the line frequency.

For 60 Hz: each cycle is 1/60 ≈ 16.66 ms therefore each cycle includes (16.66 ms)/(125 µs) ≈ 133.33 samples

For 50 Hz: each cycle is 1/50 = 20 ms therefore each cycle includes (20 ms)/(125 µs) = 160 samples

 

The HDPM6000 waveform capture uses a fixed buffer length of total 2048 samples per waveform, regardless of frequency or module type.

At 60 Hz, 2048 samples at 133.33 samples/cycle equals 15.36 cycles. -> sampling × cycles = 133.33 × 15.36

At 50 Hz, 2048 samples at 160 samples/cycle equals 12.8 cycles. -> sampling × cycles = 160 × 12.8

 

The waveform capture format of is a fixed and cannot be changed.

 

Trigger is event‑based, with 2/3 pre‑event, and waveforms are captured when:

Voltage swell or sag crosses an RMS threshold
Overcurrent or tripped breaker conditions occur
A manual “Force Capture” is issued

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-04-27 04:47 PM . Last Modified: ‎2026-04-27 11:06 PM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-27 04:47 PM

Hi @Mehran_Mehrnia 

 

 

Thank you for your prompt reply.

I now understand the HDPM6000’s waveform format, and I have a few additional questions:

 

・How many waveforms can the HDPM6000 store?
・Is the number of waveforms limited only by the capacity of the 64GB microSD card?
・Does the HDPM6000 have onboard storage in addition to the microSD card,

 or are all waveform and log data saved to the 64GB microSD card?
・Could you also let me know the size limits for the various types of data?

・Do these limits differ depending on the data type?

 

Regards,

Okada

 

 

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-30 12:58 PM

0 Likes
1
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-30 12:58 PM

Hi @T.Okada 

 

You're welcome and thank you for your patience while I waited for confirmation from the hardware team.

Please see my comments below:

 

・How many waveforms can the HDPM6000 store?

- The meter supports a maximum of 1,024 waveform entries. Once this limit is reached, waveform storage rolls over, and the oldest entries are overwritten.

Mehran_Mehrnia_0-1777577140360.png

 

・Is the number of waveforms limited only by the capacity of the 64GB microSD card?

- No, the 1024 entries are fixed and are independent of the SD card size, the connected module type, and the associated channels.


・Does the HDPM6000 have onboard storage in addition to the microSD card, or are all waveform and log data saved to the 64GB microSD card?
- All waveform captures, data logs and records are stored exclusively on the microSD card. The HDPM6000 internal onboard memory (RAM/flash) is used only for real‑time processing, temporary buffering, and Energy accumulation calculation.

・Could you also let me know the size limits for the various types of data?

- As for data logging, the meter can store a maximum of 120 (or 121) registers in INT16 format, or 60 registers in INT32 format, across 20 available logs, with a maximum of 65,535 log entries, which means:
20 logs x 65535 entries for each x (120 16-bit registers + timestamp)

Mehran_Mehrnia_1-1777578005949.png

Mehran_Mehrnia_2-1777578165683.png

As for waveform data, the meter can store a maximum of 1,024 waveforms. The file size of each waveform file depends on the number of channels in the connected branch module. For example, for one S24 module, a single waveform file is approximately 400 kB, resulting in a total storage requirement of 1,024 × 400 kB.

 

・Do these limits differ depending on the data type?

- As mentioned above, it is limited to the fixed number of entries.


Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-05-01 04:20 AM

0 Likes
0
888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-01 04:20 AM

HI @Mehran_Mehrnia 

 

Thank you for your kind reply!

 Your detailed explanation, along with the image capture, helped deepen my understanding of the HDPM6000’s logging and its capacity limitations.

Regards,

Okada

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore