Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the Number of CTs per branch circuit for HDPM in a configuration that takes single-phase branches from a three-phase, three-wire circuit

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the Number of CTs per branch circuit for HDPM in a configuration that takes single-phase branches from a three-phas...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-11 12:07 AM

0 Likes
9
1439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-11 12:07 AM

Regarding the Number of CTs per branch circuit for HDPM in a configuration that takes single-phase branches from a three-phase, three-wire circuit

Hi, 

 

We are considering applying HDPM to a panel where the main bus is a three-phase, three-wire (R, S, T) circuit that branches into individual single-phase circuits. In this case, we believe that two CTs are required per branch circuit for power measurement. However, if we only use the current value and do not use other measurement values (even if they are not measured accurately), is it possible to use just one CT per branch circuit? If this is difficult due to specifications or settings, please let us know.

 

Regards,

@T.Okada 

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-13 10:38 AM . Last Modified: ‎2025-11-13 05:13 PM

0 Likes
2
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-13 10:38 AM

Hi @Miyai @T.Okada 

 

When the meter is configured as a 3-phase Delta system, as shown in the installation guide, it (HEAD Unit) uses the Two-Wattmeter Method. In this method, phases 1 and 3 are measured relative to phase 2, which is connected to the reference N terminal:

Mehran_Mehrnia_0-1762985125873.png

aa) In the image you shared, each circuit uses two channels: one measuring the CT for phase 1 (L1–L2) and the other for phase 3 (L3–L2). Therefore, if you need to monitor 42 circuits, you will require 84 channels.

 

bb) In Delta mode, under Channel Cfg tab, each branch needs one CT in order calculate correctly the total W and kWh of the related 3 phase Delta circuit. Therefore you need to configure the channels as below. In this example, the 3 channel circuit is considered as circuit 1:

Mehran_Mehrnia_4-1763081694985.png

 

cc) As I tested, in 3 phase, Delta mode, it's not possible to have each channels' parameter individually:

 

Mehran_Mehrnia_1-1763081162588.png

In this configuration, only in 3-phase Wye mode, whether channels are bundled into a single circuit or configured individually, can the channel parameters be measured and displayed:

Mehran_Mehrnia_0-1763082796689.png

 

Mehran_Mehrnia_3-1763081333220.png

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 9
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-11 06:42 PM

0 Likes
2
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-11 06:42 PM

Hi @T.Okada 

 

Your panel uses a three-phase, three-wire (Delta) main bus, and you are taking single-phase branches from it. This is an uncommon setup for general branch circuits.


Measuring the three-phase main circuit: A three-phase, three-wire main circuit requires two CTs (connected on any two of the three phases) for accurate power (kW, kWh) measurement using the Two-Wattmeter Method.

 

The primary goal of the HDPM6000 is power monitoring. It is fundamentally an energy and power quality meter designed to calculate real power (kW) and energy (kWh), which requires both voltage and current measurements.

 

If the connection is not single-phase, three-wire (split-phase) but instead a single-phase, two-wire branch circuit, for example, where branch wire 1 (Phase R) carries current to the load and branch wire 2 (Phase S) returns current from the load, you are dealing with one current path. In this case, using one CT is sufficient for measuring amperage, provided you configure the HDPM channel to reference the correct phase-to-phase voltage (e.g., R–S) so it can calculate kW and kWh based on that single current reading.

 

This one-CT rule works only for single-phase, two-wire circuits. It does not work for Three-Phase, Three-Wire Circuit (Main Bus).

 

Best Regards,

-Mehran

L3 Expert Advanced metering 

Reply
Miyai
Miyai
Contributor

Posted: ‎2025-11-12 12:28 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-12 12:28 AM

Hi @Mehran_Mehrnia 

 

I'd like some advice on this matter.

I would like to measure V, I, W, and kWh of 42 circuits using configuration below, so I would appreciate some advice.

 

aa) If I want to measure 42 circuits, do I need to purchase an 84-circuit R unit? Or can a 42-circuit device handle it?

 

bb) Is it correct that I understand that one CT is required for one circuit as shown in the diagram below?

 

cc) Can I configure each circuit to measure power and energy separately? I've tried various settings but I can't get the power/energy consumption for each circuit to be displayed.

 

 

Miyai_0-1762936044184.png

 

 

Best regards,

Miyai

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-12 12:44 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-12 12:44 AM

Hi @Mehran_Mehrnia 

 

Thank you for your prompt reply.

 

I understand the setup for monitoring only the current on a single‑phase, two‑wire branch circuit. In this case, if I want to reference the R–S phase‑to‑phase voltage, do I need to use two CT ports on the HDPM6000R, or can I use just one? I believe one CT port would remain unused because the "Exp phase" setting cannot be configured to 1–2, 2–3, or 3–1; it can only be set to 1, 2, or 3.

Best Regards,

Okada

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-13 10:38 AM . Last Modified: ‎2025-11-13 05:13 PM

0 Likes
2
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-13 10:38 AM

Hi @Miyai @T.Okada 

 

When the meter is configured as a 3-phase Delta system, as shown in the installation guide, it (HEAD Unit) uses the Two-Wattmeter Method. In this method, phases 1 and 3 are measured relative to phase 2, which is connected to the reference N terminal:

Mehran_Mehrnia_0-1762985125873.png

aa) In the image you shared, each circuit uses two channels: one measuring the CT for phase 1 (L1–L2) and the other for phase 3 (L3–L2). Therefore, if you need to monitor 42 circuits, you will require 84 channels.

 

bb) In Delta mode, under Channel Cfg tab, each branch needs one CT in order calculate correctly the total W and kWh of the related 3 phase Delta circuit. Therefore you need to configure the channels as below. In this example, the 3 channel circuit is considered as circuit 1:

Mehran_Mehrnia_4-1763081694985.png

 

cc) As I tested, in 3 phase, Delta mode, it's not possible to have each channels' parameter individually:

 

Mehran_Mehrnia_1-1763081162588.png

In this configuration, only in 3-phase Wye mode, whether channels are bundled into a single circuit or configured individually, can the channel parameters be measured and displayed:

Mehran_Mehrnia_0-1763082796689.png

 

Mehran_Mehrnia_3-1763081333220.png

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Miyai
Miyai
Contributor

Posted: ‎2025-11-13 09:22 PM

0 Likes
0
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-13 09:22 PM

Hi @Mehran_Mehrnia 

 

Thanks for your advice.

I understand.

 

 

Best regards,

Miyai

Reply
Miyai
Miyai
Contributor

Posted: ‎2026-05-20 06:44 PM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-20 06:44 PM

Hi, @Mehran_Mehrnia 

 

I'd like some more advice.
This configuration is three-phase delta system.

 

aa) Is my understanding correct that each circuit from C1 to C3 requires 1CT?
      The measurement items are assumed to be V, I, W, PF, and kWh.

 

bb) If THDi measurement is required for each phase in the C1 to C3 circuit, are 2CTs needed for each circuit?


cc) Is there any problem with mixing C1 through C4 together?

 

dd) Regarding the C4 circuit, is 3CT required in the case of a three-phase branch?
The measurement items are assumed to be V, I, W, PF, and kWh.

 

Miyai_0-1779327653984.png

 

Best regards,

Miyai

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-05-21 09:17 AM

0 Likes
1
842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-21 09:17 AM

Hi @Miyai 

 

aa) Even though each of C1 to C3 is shown as a single‑phase branch derived from the delta bus, the way the HDPM6000 is designed means that each channel would need its own CT, although they would measure the same value.

 

bb) As mentioned above, 2 CTs are required.


cc) The channel configuration looks correct. Mixing circuits (C1–C4) is allowed in the HDPM6000 when each circuit is properly grouped and phase-mapped.

 

dd) Correct. For C4 (3-phase branch), as explained in aa, 3 CTs are recommended to enable full metering, including per-phase current, THDi, etc.


Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Miyai
Miyai
Contributor

Posted: ‎2026-05-24 06:13 PM

0 Likes
0
794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-24 06:13 PM

Hi @Mehran_Mehrnia 

 

Thanks for your advice.

 

Do you know of any documentation on examples of HDPM6000 and CT combinations?

I checked the manuals for the head unit and R unit, but I couldn't find any examples of CT connection circuits.

 

Best regards,

Miyai

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-05-25 05:18 PM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-25 05:18 PM

Hi @Miyai 

 

There is no detailed example-based CT wiring guide specifically for HDPM6000 in current manuals. Each measurement channel that is intended to monitor current per each phase must be connected to an appropriate CT input on the branch module.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore