Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the Nominal Voltage setting on the web interface of the HDPM6000 head unit

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the Nominal Voltage setting on the web interface of the HDPM6000 head unit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-07-08 02:03 AM

0 Likes
2
461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-08 02:03 AM

Regarding the Nominal Voltage setting on the web interface of the HDPM6000 head unit

Hi,

 

There is a Nominal Voltage setting under the General Settings tab on the HDPM6000 head unit’s web interface. Which functions use this setting? Since there are voltage threshold settings in items like waveform capture and alarms, I’m not sure what feature this Nominal Voltage is used for and would like to confirm.

 

Also, when configuring it, should we set it based on the main supply type as with the ION9000—i.e., use line-to-line voltage for DELTA, and phase-to-neutral voltage for Wye or split?

 

Regards,

Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-08 10:38 AM . Last Modified: ‎2026-07-17 07:39 AM

1 Like
1
444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-08 10:38 AM

Hi @T.Okada 


As for the role of the Nominal Voltage setting, because alarm and waveform capture thresholds are configured using absolute engineering units (Vrms and Arms), the Nominal Voltage setting under General Settings does not appear to directly alter these trigger points.

Instead, it serves as the baseline system reference for Power Quality analytics such as Harmonics and Displacement Power Factor(DPF), and baseline energy health diagnostics.

As stated in the Installation guide: the Nominal Voltage is the approximate voltage of the service the Head Unit is monitoring. This is the line to neutral voltage for services with a neutral, or the line to line voltage for delta.

Wye / Split-Phase Systems: Configure Nominal Voltage as Phase-to-Neutral (VL-N) (e.g., 120V or 277V).
Delta Systems: Configure Nominal Voltage as Phase-to-Phase (VL-L) (e.g., 208V or 480V).

Matching the system topology ensures that any harmonics, unbalance or health calculations derived from that Nominal Voltage baseline align with what the physical voltage taps are actually measuring.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-08 10:38 AM . Last Modified: ‎2026-07-17 07:39 AM

1 Like
1
444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-08 10:38 AM

Hi @T.Okada 


As for the role of the Nominal Voltage setting, because alarm and waveform capture thresholds are configured using absolute engineering units (Vrms and Arms), the Nominal Voltage setting under General Settings does not appear to directly alter these trigger points.

Instead, it serves as the baseline system reference for Power Quality analytics such as Harmonics and Displacement Power Factor(DPF), and baseline energy health diagnostics.

As stated in the Installation guide: the Nominal Voltage is the approximate voltage of the service the Head Unit is monitoring. This is the line to neutral voltage for services with a neutral, or the line to line voltage for delta.

Wye / Split-Phase Systems: Configure Nominal Voltage as Phase-to-Neutral (VL-N) (e.g., 120V or 277V).
Delta Systems: Configure Nominal Voltage as Phase-to-Phase (VL-L) (e.g., 208V or 480V).

Matching the system topology ensures that any harmonics, unbalance or health calculations derived from that Nominal Voltage baseline align with what the physical voltage taps are actually measuring.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-07-20 05:28 PM

0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-20 05:28 PM

Hi @Mehran_Mehrnia 

 

Thank you for your kind reply!

 

Regards,

Okada

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore