Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding limitation of the daisy chain connection of HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding limitation of the daisy chain connection of HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-09-25 02:22 AM

0 Likes
5
331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-25 02:22 AM

Regarding limitation of the daisy chain connection of HDPM6000

Hello,

 

I would like to confirm the “Maximum number of concurrent Modbus TCP connections” listed as “25” in the HDPM6000 specifications. Does this refer to the maximum number when HDPM6000 units are connected in a daisy-chain? If they are connected in a star topology, is there effectively no limitation?

Also, I understand that the typical length limit for communication over LAN cables is about 100 m. Could you explain how this applies when connecting HDPM units in a daisy-chain? For example, if every segment between devices in the daisy-chain is under 100 m, would continuous, stable communication be possible—similar to using hubs or repeaters—even if the total length across 25 daisy-chained units is 1,000 m?

Regards,

Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-28 08:47 AM

1 Like
1
283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:47 AM

Hi @T.Okada 

 

1. Regarding the 25 Concurrent Connections and 600 Units on a Network

Yes, your understanding is correct. The specification of 25 concurrent Modbus TCP connections refers to the maximum number of simultaneous client connections that a single HDPM6000 head unit can support. It does not limit the number of HDPM6000 units that can exist on the same Ethernet network.

 

Therefore, having a large number of HDPM6000 units on the same network, including hundreds of devices, is possible provided the overall network infrastructure, IP addressing scheme, and supervisory system are designed to support that number of devices. From the HDPM6000 perspective, the 25-connection specification does not impose a limit on the total number of meters deployed on the network.

 

2. Regarding Daisy-Chain Length and Device Count

For Ethernet daisy-chain installations, each individual cable segment between adjacent HDPM6000 units should comply with the Ethernet limitation of 100 m (328 ft).

 

Based on the published HDPM6000 documentation, and as Charles mentioned, we are not aware of a specified maximum number of HDPM6000 head units that may be connected in a single Ethernet daisy chain. However, this should not be interpreted as an unlimited topology. Practical limits will depend on the overall network design and communications performance requirements.

 

Additionally, because a daisy-chain topology relies on intermediate devices to maintain communication to downstream devices, the loss of power, failure, or disconnection of a device within the chain may interrupt communications to the many devices located farther downstream.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-25 09:31 AM . Last Modified: ‎2026-09-25 09:31 AM

1 Like
2
319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-25 09:31 AM

Hi @T.Okada 

 

 

The specification "Maximum number of concurrent Modbus TCP connections: 25" refers to the maximum number of simultaneous Modbus TCP client connections that a single HDPM6000 can support. This limitation is independent of the network topology and applies whether the meters are connected in a star or daisy-chain configuration.

 

Regarding Ethernet daisy-chaining, the dual Ethernet ports on the HDPM6000 allow the device to forward Ethernet traffic similarly to an embedded switch. For 10/100BASE-TX Ethernet networks, each cable segment between adjacent devices should comply with the Ethernet standard maximum length of 100 m (328 ft).

 

Therefore, a total network distance greater than 100 m may be achieved in a daisy-chain arrangement, provided that each individual segment remains within the Ethernet specification. However, overall network performance will also depend on factors such as traffic loading, bandwidth utilization, and overall network design.

 

Additionally, in a daisy-chain topology, each HDPM6000 acts as a communication pass-through device. If an intermediate unit loses power, experiences a fault, or is physically disconnected, communication with all downstream devices in that chain may be interrupted until the connection is restored.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-09-28 12:31 AM

1 Like
1
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 12:31 AM

Hi @Mehran_Mehrnia 

 

Regarding “the maximum number of simultaneous Modbus TCP client connections that a single HDPM6000 can support,” you’re not saying that only 25 HDPM units can physically exist on the same network. Rather, you mean that a single HDPM cannot establish Modbus connections with, for example, 26 master devices at the same time, correct?

 

So it should be perfectly fine to have, for instance, 600 HDPM units on the same network, with a single master communicating individually with each HDPM over Modbus. That configuration is entirely acceptable, right?

 

Also, just to confirm: for HDPM daisy-chain connections, as long as the length between each device is kept under 100 m, there’s effectively no overall length limit. Is it correct that there is no specific limit on the number of devices that can be connected in a single daisy chain?

 

Regards,

Okada

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-09-28 08:16 AM

1 Like
0
286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:16 AM

Hello @T.Okada 

"600 HDPM units on the same network, with a single master communicating individually with each HDPM over Modbus." - Correct, this can be fine from perspective of the HDPM6000.

 

"for HDPM daisy-chain connections" - Each HDPM6000 with be a switch in the network, the network can handle having multiple switches. Note that all traffic for the daisy chain will flow through the first meter, all traffic - 1 will flow through the second meter. Eventually there will be a bottle neck and you will notice a drop in communication performance.

 

Before you ask, no there is no specific number that I can give, factors outside the meter will play a much bigger role, network speeds, quality of network cables, Electromagnetic noise in environment etc. Also the definition of performance can differ between each system. Asking for data once a minute would be very different than asking for data every 10 seconds. Also the amount of data and number of requests to collect all the data  would also be a factor to consider. 

 

This is not to say you can't have HDPM6000 is a daisy chain, just don't have 600 meters all 100m apart on a single loop and expect to get data from every meter once a second.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-28 08:47 AM

1 Like
1
283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-28 08:47 AM

Hi @T.Okada 

 

1. Regarding the 25 Concurrent Connections and 600 Units on a Network

Yes, your understanding is correct. The specification of 25 concurrent Modbus TCP connections refers to the maximum number of simultaneous client connections that a single HDPM6000 head unit can support. It does not limit the number of HDPM6000 units that can exist on the same Ethernet network.

 

Therefore, having a large number of HDPM6000 units on the same network, including hundreds of devices, is possible provided the overall network infrastructure, IP addressing scheme, and supervisory system are designed to support that number of devices. From the HDPM6000 perspective, the 25-connection specification does not impose a limit on the total number of meters deployed on the network.

 

2. Regarding Daisy-Chain Length and Device Count

For Ethernet daisy-chain installations, each individual cable segment between adjacent HDPM6000 units should comply with the Ethernet limitation of 100 m (328 ft).

 

Based on the published HDPM6000 documentation, and as Charles mentioned, we are not aware of a specified maximum number of HDPM6000 head units that may be connected in a single Ethernet daisy chain. However, this should not be interpreted as an unlimited topology. Practical limits will depend on the overall network design and communications performance requirements.

 

Additionally, because a daisy-chain topology relies on intermediate devices to maintain communication to downstream devices, the loss of power, failure, or disconnection of a device within the chain may interrupt communications to the many devices located farther downstream.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-10-04 10:54 PM

0 Likes
0
250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-04 10:54 PM

Hello @Mehran_Mehrnia , @Charles_Murison 

 

Thank you for your reply.

 

I understand that in a daisy-chain configuration, there should be no issue as long as the distance between each HDPM6000 unit is less than 100 meters; however, since performance depends on the environment, you cannot state the maximum number of units that can be connected.

 

Thank you.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore