Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding Pulse width of the DO option module (with PM8240)

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding Pulse width of the DO option module (with PM8240)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-07-21 02:57 AM

0 Likes
7
440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-21 02:57 AM

Regarding Pulse width of the DO option module (with PM8240)

Hi,

We are using a digital output option module on the PM8000 with the following setup:

  • Port A D1: DO output triggered by sag/swell detection (pulse width set to 40 ms)
  • Port A D2: DO output triggered by a newly created setpoint for harmonic voltage detection (pulse width set to 100 ms)

Although we have definitively configured the output module (pulse width) to:

  • 0.04 s
  • 0.10 s

both channels operate correctly at the specified durations when the input pulse to the digital output module’s Force On is the sag/swell SS1 Dist Start.

 

However, when the input pulse to Force On is from the harmonic detection

(the pulse generated when the setpoint module threshold is exceeded),

both channels produce pulses of approximately 1 second.

It’s puzzling because both cases are pulse outputs.

 

Looking closely at the event log timestamps for the DO output,

when the pulse is triggered by harmonic detection,

the outputs occur at 1-second intervals rather than 0.1 seconds.

 

Do you know what might be causing this?

Ultimately, we want:

 

  • For sag/swell detection (sag/swell module): a pulse width of 40 ms
  • For harmonic detection (setpoint module): a pulse width of 100 ms

and for each to output correctly as configured.

 

Regards,

Okada

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-07-22 10:04 AM

0 Likes
0
389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 10:04 AM

Hello @T.Okada 

Looking at the ION reference I can see the following note for Digital Output modules (ION Reference )
"Note: The pulse width is dependent on the operate period of the Digital Output Module. For example, if a Digital Output Module is operating at 1-second intervals, the pulse width will be a multiple of 1 s, rounded up from the value set in the PulseWidth register."

Digital output modules with be either 1/2 cycle or 1 second speed depending on the input(s). If all inputs are 1 second modules, the Digital output will be 1 second. If any input is high speed, module will be high speed.

 

One way to make this happen is to use a pulse merge module. The the pulse output from your setpoint module be one input to your pulse merge module then use a pulse output from a 1/2 cycle module. The pulse merge module will be 1/2 cycle so Digital output will be 1/2 cycle. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-22 12:25 PM

0 Likes
1
380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 12:25 PM

Hi @T.Okada 

 

Here's a simple example implemented based on Charles's suggestion:

Mehran_Mehrnia_0-1784748126102.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 7
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-21 08:12 AM

0 Likes
0
428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-21 08:12 AM

Hi @T.Okada 

 

The harmonic detection is derived from the Harmonics Measurement modules, which operate at a one-second update rate. According to the ION Reference, when a standard ION module is involved, the framework execution rate is limited by the slower module.

 

Since the Sag/Swell module is a High Speed module and the Harmonics Measurement module is a one-second module, harmonic-triggered outputs will naturally exhibit approximately one-second timing resolution, whereas sag/swell-triggered outputs can respond at high-speed rates. This explains the difference in the observed pulse behavior.

 

Mehran_Mehrnia_0-1784646652705.pngMehran_Mehrnia_1-1784646695480.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-07-21 08:14 AM

0 Likes
2
427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-21 08:14 AM

Hello @T.Okada ,

 

Are you able to provide some details about your framework? Ideal would be entire template but if that is not possible would be good to share Details about the inputs, including handles, and the setup registers.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-07-21 05:16 PM

0 Likes
1
415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-21 05:16 PM

Hi @Mehran_Mehrnia, @Charles_Murison 

 

Thank you for your prompt response.
I’ve attached an image with the framework details.
Given this configuration, do you have any recommendations on how to implement a 100 ms pulse width for Over-THD detection?

For reference, “THD V1–V3 Max” and “THDV High Limit” are custom modules we developed.

 

TOkada_1-1784679053603.png

 

Regards,

Okada

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-22 09:53 AM

0 Likes
0
391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 09:53 AM

Hi @T.Okada 

 

You're welcome.

 

@Charles_Murison please correct me if I am mistaken, but as previously mentioned, this behavior is related to the module's execution speed. Since the Harmonics Module, which is the source of the signal, operates at a low-speed update rate of 1 second, any modules linked to its output will also operate at the same update rate.

 

I reproduced the same scenario shown in the image. Although the PulseWidth parameter is set to 0.1 second, the Event Log records the pulse duration as 1 second, as shown below. This occurs because the pulse is generated by a source module running at a 1-second update rate, which limits the effective resolution of the pulse timing.

 

Therefore, the observed behavior is expected and is a consequence of the source module's execution rate rather than the configured PulseWidth value.

 

Mehran_Mehrnia_0-1784738714081.png

 

ION Reference: Digital Output

Mehran_Mehrnia_1-1784739139934.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-07-22 10:04 AM

0 Likes
0
390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 10:04 AM

Hello @T.Okada 

Looking at the ION reference I can see the following note for Digital Output modules (ION Reference )
"Note: The pulse width is dependent on the operate period of the Digital Output Module. For example, if a Digital Output Module is operating at 1-second intervals, the pulse width will be a multiple of 1 s, rounded up from the value set in the PulseWidth register."

Digital output modules with be either 1/2 cycle or 1 second speed depending on the input(s). If all inputs are 1 second modules, the Digital output will be 1 second. If any input is high speed, module will be high speed.

 

One way to make this happen is to use a pulse merge module. The the pulse output from your setpoint module be one input to your pulse merge module then use a pulse output from a 1/2 cycle module. The pulse merge module will be 1/2 cycle so Digital output will be 1/2 cycle. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-22 12:25 PM

0 Likes
1
381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 12:25 PM

Hi @T.Okada 

 

Here's a simple example implemented based on Charles's suggestion:

Mehran_Mehrnia_0-1784748126102.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-07-22 04:48 PM

0 Likes
0
371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-22 04:48 PM

Hi @Mehran_Mehrnia , @Charles_Murison ,

 

Thank you for the idea.
I updated the framework based on your suggestion

(using a pulse merge and a high‑speed frequency module),

and the issue is resolved.

 

Regards,

Okada

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore