Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Questions on Disabling Alarms and Configuring Breaker Trip Alarms for HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Questions on Disabling Alarms and Configuring Breaker Trip Alarms for HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
573
Mehran_Mehrnia
Mehran_Mehrnia Champion
210
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-07 11:52 PM

0 Likes
5
459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-07 11:52 PM

Questions on Disabling Alarms and Configuring Breaker Trip Alarms for HDPM6000

Hello,

I would appreciate your guidance on the following points regarding the HDPM6000:

 

1. Disabling voltage alarms
If we set both the High threshold and Low threshold to 0.0, will that effectively disable voltage alarm detection on the device?


2. Disabling current alarms for mains and branch circuits
What is the recommended method to disable current alarms for each main and branch circuit?
Would setting the rated breaker value to 0 A be an appropriate way to disable those alarms, or is there a preferred procedure?


3. Trip breaker alarm configuration
For the trip breaker current threshold, is it possible to configure different threshold values for the main and for individual circuits respectively? I can only find a single input field for the threshold.
Additionally, how can we completely disable the trip breaker alarm?


4. Availability of default parameter lists and configuration export
Is there documentation that lists the factory default settings for the HDPM6000?
With ION Setup, PQM meters allow exporting configuration to a text file. Is there a similar function on the HDPM6000 to extract a settings list from a new (factory-default) meter?

 

Best regards,

Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-10 12:52 PM . Last Modified: ‎2026-08-10 12:57 PM

2 Likes
2
421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-10 12:52 PM

Hi  @T.Okada 

 

There is no dedicated enable/disable toggle button for alarms in the web interface, disabling requires adjusting user-defined thresholds and delays.

 

Mehran_Mehrnia_2-1786390632391.png

 

1. Disabling Voltage Alarms

  • Effect of 0.0 V threshold: Setting the Low Threshold to 0.0 V disables low-voltage alarms, but setting the High Threshold to 0.0 V causes continuous High Voltage Alarms as line voltage exceeds 0.0 V.

  • Recommended method: Set Low Threshold to 0.0 V and set High Threshold to an arbitrarily high value well above maximum system voltage.

2. Disabling Current Alarms (Mains & Branch Circuits)

  • Recommended method for active channels: Max out the warning and alarm threshold percentages (or assign an arbitrarily large breaker size) so normal operating current never reaches the alarm setpoint.

  • Recommended method for unused channels: For any unmonitored circuits, navigate to the Channel Cfg tab and set the CT Type to "Unused".

  • Effect of 0 A breaker size: Setting Breaker Size to 0 A is out of range and must be equal or more than one. Since the current alarms are percentage-based, lower values causing immediate over-current alarms on active loads.

3. Trip Breaker Alarm Configuration

  • Per-circuit thresholding: Not supported; Tripped Breaker Current and Delay are global settings applied across the system.

  • Disabling method: Set the global Tripped Breaker Current threshold to a value higher than maximum expected load current.

4. Default Parameter Lists & Configuration Export

  • Configuration Export Function: Unlike PQM meters using ION Setup to generate text files, the HDPM6000 uses the HDPM6000 Manager software. By connecting to a unit, you can click Download Configuration... to extract and save the entire device parameter set into a .cfg file. This .cfg file can be archived or uploaded to other units.

Mehran_Mehrnia_1-1786390577904.png

 


 

  • Factory Default Documentation: HDPMs are often shipped with a complex, customer-specific configuration defined in a configuration file. Using a default configuration would likely be incompatible with the customer's system and could prevent communication with the meter. The original customer-specific configuration can be restored by reloading the configuration file.
    Factory default parameters such as default IP 10.10.10.4, default credentials, default RS-485 speed 115200, Zero Threshold 0.09%, and Energy Resolution 1 Wh, ,etc are detailed throughout the commissioning sections of the HDPM6000 Installation Guide.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-17 06:46 PM . Last Modified: ‎2026-08-17 06:48 PM

1 Like
0
317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-17 06:46 PM

Hi @T.Okada 

 

You're welcome.

 

Breaker Size (A) is independent per Channel and configured individually for each PQM current channel and branch circuit by toggling the Channels / PQM views('Channels/PQM' button on the top right in the Alarm page). Modifying Breaker Size (A) does not affect display functions and only warning/alarm thresholds.

 

Tripped Breaker Current is a global Threshold which serves as a single global parameter across the meter and there are no separate numerical thresholds for mains versus branch circuits.

 

That is correct. It is Evaluated independently per phase/channel and is not against the sum of branch currents.

 

Just to clarify, the Tripped Breaker alarm is only triggered when two sequential conditions on a channel are met:

  • 1. The measured current must first exceed the threshold to arm the alarm state.

  • 2. The measured current must then drop to 0 A while line voltage remains present.

 

Best Regards,

-Mehran
L3 Expert Advanced metering

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-10 12:52 PM . Last Modified: ‎2026-08-10 12:57 PM

2 Likes
2
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-10 12:52 PM

Hi  @T.Okada 

 

There is no dedicated enable/disable toggle button for alarms in the web interface, disabling requires adjusting user-defined thresholds and delays.

 

Mehran_Mehrnia_2-1786390632391.png

 

1. Disabling Voltage Alarms

  • Effect of 0.0 V threshold: Setting the Low Threshold to 0.0 V disables low-voltage alarms, but setting the High Threshold to 0.0 V causes continuous High Voltage Alarms as line voltage exceeds 0.0 V.

  • Recommended method: Set Low Threshold to 0.0 V and set High Threshold to an arbitrarily high value well above maximum system voltage.

2. Disabling Current Alarms (Mains & Branch Circuits)

  • Recommended method for active channels: Max out the warning and alarm threshold percentages (or assign an arbitrarily large breaker size) so normal operating current never reaches the alarm setpoint.

  • Recommended method for unused channels: For any unmonitored circuits, navigate to the Channel Cfg tab and set the CT Type to "Unused".

  • Effect of 0 A breaker size: Setting Breaker Size to 0 A is out of range and must be equal or more than one. Since the current alarms are percentage-based, lower values causing immediate over-current alarms on active loads.

3. Trip Breaker Alarm Configuration

  • Per-circuit thresholding: Not supported; Tripped Breaker Current and Delay are global settings applied across the system.

  • Disabling method: Set the global Tripped Breaker Current threshold to a value higher than maximum expected load current.

4. Default Parameter Lists & Configuration Export

  • Configuration Export Function: Unlike PQM meters using ION Setup to generate text files, the HDPM6000 uses the HDPM6000 Manager software. By connecting to a unit, you can click Download Configuration... to extract and save the entire device parameter set into a .cfg file. This .cfg file can be archived or uploaded to other units.

Mehran_Mehrnia_1-1786390577904.png

 


 

  • Factory Default Documentation: HDPMs are often shipped with a complex, customer-specific configuration defined in a configuration file. Using a default configuration would likely be incompatible with the customer's system and could prevent communication with the meter. The original customer-specific configuration can be restored by reloading the configuration file.
    Factory default parameters such as default IP 10.10.10.4, default credentials, default RS-485 speed 115200, Zero Threshold 0.09%, and Energy Resolution 1 Wh, ,etc are detailed throughout the commissioning sections of the HDPM6000 Installation Guide.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-15 06:19 PM

1 Like
1
363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-15 06:19 PM

Hello @Mehran_Mehrnia,

 

Thank you for your detailed reply!

 

I have a question about disabling the current alarms.

 

You recommend setting a large breaker rated current to disable current alarms, but could that affect any other current-related display functions? Or is the rated current setting used only for alarm thresholds?

 

Regards,

Okada

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-15 06:33 PM . Last Modified: ‎2026-08-15 06:33 PM

0 Likes
0
361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-15 06:33 PM

Hello @Mehran_Mehrnia,

 

I have more questions about the tripped breaker current threshold.

 

Is the value only for branch circuits? or both of the main and branch circuits?

If that’s the case, I would prefer to have separate thresholds for the main and branch circuits.

 

The trip breaker threshold isn’t applied to the sum of the branch circuit currents, correct?

Similar to how the “Circuits” option works in the Summary Current settings.
If so, I think I should set a threshold large enough—exceeding the main breaker size—when configuring it to effectively disable this feature.

Regards,

Okada

 

 

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-17 06:46 PM . Last Modified: ‎2026-08-17 06:48 PM

1 Like
0
318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-17 06:46 PM

Hi @T.Okada 

 

You're welcome.

 

Breaker Size (A) is independent per Channel and configured individually for each PQM current channel and branch circuit by toggling the Channels / PQM views('Channels/PQM' button on the top right in the Alarm page). Modifying Breaker Size (A) does not affect display functions and only warning/alarm thresholds.

 

Tripped Breaker Current is a global Threshold which serves as a single global parameter across the meter and there are no separate numerical thresholds for mains versus branch circuits.

 

That is correct. It is Evaluated independently per phase/channel and is not against the sum of branch currents.

 

Just to clarify, the Tripped Breaker alarm is only triggered when two sequential conditions on a channel are met:

  • 1. The measured current must first exceed the threshold to arm the alarm state.

  • 2. The measured current must then drop to 0 A while line voltage remains present.

 

Best Regards,

-Mehran
L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-24 10:45 PM

0 Likes
0
188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-24 10:45 PM

Hi @Mehran_Mehrnia,

 

Thank you for your reply!

and your additional clarification is also very helpful to us!

 

Regards,

Okada

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore