Continue
  • My Subscriptions
  • Events
Powertags not giving off data on ION SETUP
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Powertags not giving off data on ION SETUP
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
PowerLogic™ PowerTag
jedzruiz1985
jedzruiz1985
Explorer
Posted: ‎2025-12-18 06:31 PM
625
Hi Xperts,
For the latest ION SETUP, just wondering why the power tags are not showing the readings. Is this a bug?
Device is set at Modbus RTU under a Modbus TCP Site. Status shows "On-Line" but there are no readings. Please see below configs for OFFICE-DB (Power tag M250-3P)
I tried other power tags, same issue. Which is the correct device type to use for powertags (I used modbus RTU from a TCP site which is a panel server)
Thanks and best regards,
Jedz
  • Thumbnail of PowerLogic™ PowerTag
View products (1)
  • PowerTag Energy
Charles_Murison
Champion
Posted: ‎2025-12-19 08:48 AM
Hello @jedzruiz1985 ,
ION Setup is not developed with support for PowerTag devices. While it is true that you can add a Modbus device, either TCP or RTU, there is another selection needed called the display. This tells ION Setup what Modbus addresses to use. When I look at my ION Setup I do not see any display option for PowerTag devices.
I believe EcoStruxure Power Commission (EPC) software is what you need to configure the devices.
Charles
Charles_Murison
Champion
Charles
jedzruiz1985
jedzruiz1985
Explorer
Posted: ‎2026-01-14 03:38 PM
Thanks Charles