Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Hello team
I have a power logic ION 7550 meter which is stuck in a boot loop after a normal power interruption and restoration. Attempts to power cycle severally have been unsuccessful, attempt to perform firmware upgrade but the meter is not detected on the ION software, front keys on the panel are unresponsive. I have attached a screenshot with the boot error displayed. Any assistance is highly appreciated
Link copied. Please paste this link to share this article on your social media post.
Hi @ACTOM-EA
As mentioned in the similar post Ion7650 boot error, Boot Error indicates a Flash memory error.
Boot Errors cannot be recovered in the field, and will require a repair at the factory, however the ION7550/ION7650 series has officially reached its End of Support life stage as of September 2024. Consequently, factory repair and reprogramming services are no longer available for this model.
In rare cases VRS may be able to advise on any remaining options. I recommend contacting local technical support or Victoria Return Services at VRS@schneider-electric.com to confirm whether any support is still possible.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @ACTOM-EA
As mentioned in the similar post Ion7650 boot error, Boot Error indicates a Flash memory error.
Boot Errors cannot be recovered in the field, and will require a repair at the factory, however the ION7550/ION7650 series has officially reached its End of Support life stage as of September 2024. Consequently, factory repair and reprogramming services are no longer available for this model.
In rare cases VRS may be able to advise on any remaining options. I recommend contacting local technical support or Victoria Return Services at VRS@schneider-electric.com to confirm whether any support is still possible.
Best Regards,
-Mehran
L3 Expert Advanced metering
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.