Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Power Quality Meter and power meter Loss of communication .

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Power Quality Meter and power meter Loss of communication .
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
RAHUL1
RAHUL1
Explorer

Posted: ‎2026-10-16 02:00 AM

0 Likes
3
224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-16 02:00 AM

Power Quality Meter and power meter Loss of communication .

Can we assign DO for commination fail with ION setup for PM8000 and PM5320.  

Labels
  • Labels:
  • ION8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RobGraham
RobGraham Champion
Champion

Posted: ‎2026-10-16 04:12 AM . Last Modified: ‎2026-10-16 04:25 AM

0 Likes
1
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-16 04:12 AM

I have never done this myself, so if someone else has, take their advice first.  I don't see any general "network status" registers at a glance.  I can imagine a couple of ways of doing this, though, depending on what capabilities the communication client has.

 

The simplest method would be to use the Modbus Import Module, Modbus Master Device Module, or Modbus Export Module to read or write a register on the client.  Each of those modules has a Status output that could be tied to a digital output.

 

Alternately, you could use the Modbus Slave Module as a dead man's switch if your client can only write registers.  Configure the module in Unsigned 16B Input Mode and have the client write a different number to the register, say every five seconds.  Take the output of this module to an Arithmetic Module and use the formula S1 = P1(5), which will set TRUE if the current value is equal to the value five seconds ago, indicating the value has not been written.  (You may need to wrap this in an IF statement--I don't remember.)  Finally, take this value to a Convert Module to change it into a boolean that can drive the digital output.

 

All of this would need to be tested and modified as needed.  Good luck!

 

Edit:  This only works for an ION meter.  I don't know of a way to do this on a PM5000.

See Answer In Context

Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-10-20 09:47 PM

0 Likes
0
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-20 09:47 PM

Hi @RAHUL1 Regarding PM5320 meter: The meter has Ethernet Modbus TCP/IP and configurable digital I/O/alarms. However, there is no general network communication status registers / communication-failure alarm that can be assigned to a DO.
Only available option to monitor it at the meter end is by using the ethernet communication LEDs:

akash_das_0-1792558026302.png

 

See Answer In Context

Reply
Replies 3
RobGraham
RobGraham Champion
Champion

Posted: ‎2026-10-16 04:12 AM . Last Modified: ‎2026-10-16 04:25 AM

0 Likes
1
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-16 04:12 AM

I have never done this myself, so if someone else has, take their advice first.  I don't see any general "network status" registers at a glance.  I can imagine a couple of ways of doing this, though, depending on what capabilities the communication client has.

 

The simplest method would be to use the Modbus Import Module, Modbus Master Device Module, or Modbus Export Module to read or write a register on the client.  Each of those modules has a Status output that could be tied to a digital output.

 

Alternately, you could use the Modbus Slave Module as a dead man's switch if your client can only write registers.  Configure the module in Unsigned 16B Input Mode and have the client write a different number to the register, say every five seconds.  Take the output of this module to an Arithmetic Module and use the formula S1 = P1(5), which will set TRUE if the current value is equal to the value five seconds ago, indicating the value has not been written.  (You may need to wrap this in an IF statement--I don't remember.)  Finally, take this value to a Convert Module to change it into a boolean that can drive the digital output.

 

All of this would need to be tested and modified as needed.  Good luck!

 

Edit:  This only works for an ION meter.  I don't know of a way to do this on a PM5000.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-10-16 11:06 AM

1 Like
0
206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-16 11:06 AM

Hello @RAHUL1 

 

Rob's comments are correct, there is no network status ION register in the PM8000 meter that can give the communication status. There are many options for ION frameworks to likely do what you are asking for. The example Rob gave of writing a new value to a Modbus register is one example. I will note, you would need if statement, if(s1=P1(5),1,0)

I can't speak to the PM5000 series of meters what is possible.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2026-10-20 09:47 PM

0 Likes
0
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-20 09:47 PM

Hi @RAHUL1 Regarding PM5320 meter: The meter has Ethernet Modbus TCP/IP and configurable digital I/O/alarms. However, there is no general network communication status registers / communication-failure alarm that can be assigned to a DO.
Only available option to monitor it at the meter end is by using the ethernet communication LEDs:

akash_das_0-1792558026302.png

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore