Can we assign DO for commination fail with ION setup for PM8000 and PM5320.
Link copied. Please paste this link to share this article on your social media post.
I have never done this myself, so if someone else has, take their advice first. I don't see any general "network status" registers at a glance. I can imagine a couple of ways of doing this, though, depending on what capabilities the communication client has.
The simplest method would be to use the Modbus Import Module, Modbus Master Device Module, or Modbus Export Module to read or write a register on the client. Each of those modules has a Status output that could be tied to a digital output.
Alternately, you could use the Modbus Slave Module as a dead man's switch if your client can only write registers. Configure the module in Unsigned 16B Input Mode and have the client write a different number to the register, say every five seconds. Take the output of this module to an Arithmetic Module and use the formula S1 = P1(5), which will set TRUE if the current value is equal to the value five seconds ago, indicating the value has not been written. (You may need to wrap this in an IF statement--I don't remember.) Finally, take this value to a Convert Module to change it into a boolean that can drive the digital output.
All of this would need to be tested and modified as needed. Good luck!
Edit: This only works for an ION meter. I don't know of a way to do this on a PM5000.
Link copied. Please paste this link to share this article on your social media post.
Hi @RAHUL1 Regarding PM5320 meter: The meter has Ethernet Modbus TCP/IP and configurable digital I/O/alarms. However, there is no general network communication status registers / communication-failure alarm that can be assigned to a DO.
Only available option to monitor it at the meter end is by using the ethernet communication LEDs:
Link copied. Please paste this link to share this article on your social media post.
I have never done this myself, so if someone else has, take their advice first. I don't see any general "network status" registers at a glance. I can imagine a couple of ways of doing this, though, depending on what capabilities the communication client has.
The simplest method would be to use the Modbus Import Module, Modbus Master Device Module, or Modbus Export Module to read or write a register on the client. Each of those modules has a Status output that could be tied to a digital output.
Alternately, you could use the Modbus Slave Module as a dead man's switch if your client can only write registers. Configure the module in Unsigned 16B Input Mode and have the client write a different number to the register, say every five seconds. Take the output of this module to an Arithmetic Module and use the formula S1 = P1(5), which will set TRUE if the current value is equal to the value five seconds ago, indicating the value has not been written. (You may need to wrap this in an IF statement--I don't remember.) Finally, take this value to a Convert Module to change it into a boolean that can drive the digital output.
All of this would need to be tested and modified as needed. Good luck!
Edit: This only works for an ION meter. I don't know of a way to do this on a PM5000.
Link copied. Please paste this link to share this article on your social media post.
Hello @RAHUL1
Rob's comments are correct, there is no network status ION register in the PM8000 meter that can give the communication status. There are many options for ION frameworks to likely do what you are asking for. The example Rob gave of writing a new value to a Modbus register is one example. I will note, you would need if statement, if(s1=P1(5),1,0)
I can't speak to the PM5000 series of meters what is possible.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @RAHUL1 Regarding PM5320 meter: The meter has Ethernet Modbus TCP/IP and configurable digital I/O/alarms. However, there is no general network communication status registers / communication-failure alarm that can be assigned to a DO.
Only available option to monitor it at the meter end is by using the ethernet communication LEDs: