Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8240 I1 I2 I3 I4 connections

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8240 I1 I2 I3 I4 connections
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Rishita
Rishita Explorer
Explorer

Posted: ‎2026-10-14 11:50 PM

0 Likes
4
314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-14 11:50 PM

PM8240 I1 I2 I3 I4 connections

Hi everyone,

I have a question regarding CT wiring for a PM8240 meter in a 3 CT, 4-wire configuration using a shorting block.

The instruction sheet shows the I1-, I2-, I3-, and I4- terminals connected together to a common point. However, in most of our installations, each CT secondary negative is wired separately to the shorting block rather than being connected together.

Could someone clarify which method is correct?

  • Should all CT negatives (I1-, I2-, I3-, and I4-) be connected to a common point as shown in the manual?
  • Or should each CT negative remain separate through the shorting block?
  • How does either approach affect the meter's current measurements, residual current calculation/measurement, or overall accuracy?
Attachments
Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-10-15 08:00 AM . Last Modified: ‎2026-10-15 12:38 PM

1 Like
1
299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 08:00 AM

Hi @Rishita 

 

The manufacturer’s installation sheet requires the negative/secondary terminals (I1-, I2-, I3-, and I4-) to be tied together at a common point and connected to earth ground for safety.


In your diagram, while each CT secondary (S1,S2) should pass through separate terminals on the shorting block to allow for individual testing and shorting, the negative sides (S2) must be jumpered together either before the shorting block(your diagram) or on the meter side of the shorting block and grounded. This establishes a stable common electrical reference (return path) for the meter's internal metrology circuitry. 

In a 3CT configuration, the PM8240 relies on its internal firmware (using Kirchhoff's current law) to continuously derive the calculated neutral/residual current (I4) from the vector sum of phases I1, I2, and I3. If the common return is missing or improperly wired, the vector summation is distorted, which results in incorrect residual current, incorrect unbalance reporting, and compromised overall meter accuracy.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-10-15 11:23 AM

1 Like
1
289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 11:23 AM

Hello @Rishita ,

 

The install diagram is not the one and only way, just a recommended way that can reduce how much wire is needed to install a system. This is not to say the diagram is the one and only way.

 

There are a few things to consider.
A) Each CT needs to have 1 leg connected to ground for safety.

B) Each phase needs a path for CT current to have a return path.

C) Each current phase needs to match voltage phase.

D) Phase 4 (-) should be connected to a phase (-).

 

"Could someone clarify which method is correct?"

Both the install guide and your diagram is correct. 

"Should all CT negatives (I1-, I2-, I3-, and I4-) be connected to a common point as shown in the manual? Or should each CT negative remain separate through the shorting block?"

Both are correct, each has benefits. The way described in the install guide uses less wire overall, the way described in your diagram is easy to understand how the current flows.

"How does either approach affect the meter's current measurements, residual current calculation/measurement, or overall accuracy?"
No difference to current measurements or calculations on the meter. No difference to overall accuracy.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-10-15 08:00 AM . Last Modified: ‎2026-10-15 12:38 PM

1 Like
1
299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 08:00 AM

Hi @Rishita 

 

The manufacturer’s installation sheet requires the negative/secondary terminals (I1-, I2-, I3-, and I4-) to be tied together at a common point and connected to earth ground for safety.


In your diagram, while each CT secondary (S1,S2) should pass through separate terminals on the shorting block to allow for individual testing and shorting, the negative sides (S2) must be jumpered together either before the shorting block(your diagram) or on the meter side of the shorting block and grounded. This establishes a stable common electrical reference (return path) for the meter's internal metrology circuitry. 

In a 3CT configuration, the PM8240 relies on its internal firmware (using Kirchhoff's current law) to continuously derive the calculated neutral/residual current (I4) from the vector sum of phases I1, I2, and I3. If the common return is missing or improperly wired, the vector summation is distorted, which results in incorrect residual current, incorrect unbalance reporting, and compromised overall meter accuracy.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-10-15 11:23 AM

1 Like
1
289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 11:23 AM

Hello @Rishita ,

 

The install diagram is not the one and only way, just a recommended way that can reduce how much wire is needed to install a system. This is not to say the diagram is the one and only way.

 

There are a few things to consider.
A) Each CT needs to have 1 leg connected to ground for safety.

B) Each phase needs a path for CT current to have a return path.

C) Each current phase needs to match voltage phase.

D) Phase 4 (-) should be connected to a phase (-).

 

"Could someone clarify which method is correct?"

Both the install guide and your diagram is correct. 

"Should all CT negatives (I1-, I2-, I3-, and I4-) be connected to a common point as shown in the manual? Or should each CT negative remain separate through the shorting block?"

Both are correct, each has benefits. The way described in the install guide uses less wire overall, the way described in your diagram is easy to understand how the current flows.

"How does either approach affect the meter's current measurements, residual current calculation/measurement, or overall accuracy?"
No difference to current measurements or calculations on the meter. No difference to overall accuracy.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Rishita
Rishita Explorer
Explorer

Posted: ‎2026-10-15 10:24 PM

0 Likes
0
264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 10:24 PM

Hi @Charles_Murison,
Thank you for taking the time to clarify my query. I appreciate your response.
Reply
Rishita
Rishita Explorer
Explorer

Posted: ‎2026-10-15 10:26 PM

0 Likes
0
264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-15 10:26 PM

Hello @Mehran_Mehrnia,
Thank you for clarifying my query. I will short the terminals either before or after the shorting block

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore