Hi everyone,
I have a question regarding CT wiring for a PM8240 meter in a 3 CT, 4-wire configuration using a shorting block.
The instruction sheet shows the I1-, I2-, I3-, and I4- terminals connected together to a common point. However, in most of our installations, each CT secondary negative is wired separately to the shorting block rather than being connected together.
Could someone clarify which method is correct?
Link copied. Please paste this link to share this article on your social media post.
Hi @Rishita
The manufacturer’s installation sheet requires the negative/secondary terminals (I1-, I2-, I3-, and I4-) to be tied together at a common point and connected to earth ground for safety.
In your diagram, while each CT secondary (S1,S2) should pass through separate terminals on the shorting block to allow for individual testing and shorting, the negative sides (S2) must be jumpered together either before the shorting block(your diagram) or on the meter side of the shorting block and grounded. This establishes a stable common electrical reference (return path) for the meter's internal metrology circuitry.
In a 3CT configuration, the PM8240 relies on its internal firmware (using Kirchhoff's current law) to continuously derive the calculated neutral/residual current (I4) from the vector sum of phases I1, I2, and I3. If the common return is missing or improperly wired, the vector summation is distorted, which results in incorrect residual current, incorrect unbalance reporting, and compromised overall meter accuracy.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @Rishita ,
The install diagram is not the one and only way, just a recommended way that can reduce how much wire is needed to install a system. This is not to say the diagram is the one and only way.
There are a few things to consider.
A) Each CT needs to have 1 leg connected to ground for safety.
B) Each phase needs a path for CT current to have a return path.
C) Each current phase needs to match voltage phase.
D) Phase 4 (-) should be connected to a phase (-).
"Could someone clarify which method is correct?"
Both the install guide and your diagram is correct.
"Should all CT negatives (I1-, I2-, I3-, and I4-) be connected to a common point as shown in the manual? Or should each CT negative remain separate through the shorting block?"
Both are correct, each has benefits. The way described in the install guide uses less wire overall, the way described in your diagram is easy to understand how the current flows.
"How does either approach affect the meter's current measurements, residual current calculation/measurement, or overall accuracy?"
No difference to current measurements or calculations on the meter. No difference to overall accuracy.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Rishita
The manufacturer’s installation sheet requires the negative/secondary terminals (I1-, I2-, I3-, and I4-) to be tied together at a common point and connected to earth ground for safety.
In your diagram, while each CT secondary (S1,S2) should pass through separate terminals on the shorting block to allow for individual testing and shorting, the negative sides (S2) must be jumpered together either before the shorting block(your diagram) or on the meter side of the shorting block and grounded. This establishes a stable common electrical reference (return path) for the meter's internal metrology circuitry.
In a 3CT configuration, the PM8240 relies on its internal firmware (using Kirchhoff's current law) to continuously derive the calculated neutral/residual current (I4) from the vector sum of phases I1, I2, and I3. If the common return is missing or improperly wired, the vector summation is distorted, which results in incorrect residual current, incorrect unbalance reporting, and compromised overall meter accuracy.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @Rishita ,
The install diagram is not the one and only way, just a recommended way that can reduce how much wire is needed to install a system. This is not to say the diagram is the one and only way.
There are a few things to consider.
A) Each CT needs to have 1 leg connected to ground for safety.
B) Each phase needs a path for CT current to have a return path.
C) Each current phase needs to match voltage phase.
D) Phase 4 (-) should be connected to a phase (-).
"Could someone clarify which method is correct?"
Both the install guide and your diagram is correct.
"Should all CT negatives (I1-, I2-, I3-, and I4-) be connected to a common point as shown in the manual? Or should each CT negative remain separate through the shorting block?"
Both are correct, each has benefits. The way described in the install guide uses less wire overall, the way described in your diagram is easy to understand how the current flows.
"How does either approach affect the meter's current measurements, residual current calculation/measurement, or overall accuracy?"
No difference to current measurements or calculations on the meter. No difference to overall accuracy.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @Mehran_Mehrnia,
Thank you for clarifying my query. I will short the terminals either before or after the shorting block