Hi,
can you please advise on this .
The EPC intends to use outputs from the proposed PM8000 as inputs to the PPC (Power Plant Controller) for control purposes. As part of their requirements, they have specified an update rate of less than 50 ms for real-time values received from the PM8000.
My understanding is that the PM8000 updates measurements every ½ cycle; however, I would appreciate your guidance on whether this update rate applies to the real-time measurement values made available via communications, or whether it relates to internally calculated values.
I need to ensure that we can confidently confirm the maximum delay of the real-time values being provided by the PM8000 and whether the <50 ms requirement can be met.
Could you please advise,
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
As noted in similar community posts, communications in ION-based meters operate as a lower-priority task compared to core functions like metering, logging, and power quality processing. Consequently, communication latency is variable and non-deterministic particularly when the meter CPU is busy with heavy tasks. Schneider Electric does not specify or guarantee that a measured value can be delivered via Modbus or Ethernet within a fixed time frame, such as <50 ms.
ION meters like the PM8000 update measurements internally every ½ cycle (approximately 8.3 ms at 60 Hz or 10 ms at 50 Hz). However, this update rate applies exclusively to the meter's internal calculation engine and High-Speed (HS) measurement modules at the module level, it does not apply to external communications.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
As noted in similar community posts, communications in ION-based meters operate as a lower-priority task compared to core functions like metering, logging, and power quality processing. Consequently, communication latency is variable and non-deterministic particularly when the meter CPU is busy with heavy tasks. Schneider Electric does not specify or guarantee that a measured value can be delivered via Modbus or Ethernet within a fixed time frame, such as <50 ms.
ION meters like the PM8000 update measurements internally every ½ cycle (approximately 8.3 ms at 60 Hz or 10 ms at 50 Hz). However, this update rate applies exclusively to the meter's internal calculation engine and High-Speed (HS) measurement modules at the module level, it does not apply to external communications.
Best Regards,
-Mehran
L3 Expert Advanced metering