PM8000 "invalid intervals" for power quality module

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
RdM
Ensign
Ensign
0 Likes
3
742

PM8000 "invalid intervals" for power quality module

Hi, 

I have a PM8000 installed onsite with latest firmware uploaded. Large number of invalid intervals listed for weekly and daily intervals for IEEE519 diagram and EN50160 diagrams for Harmonics, Frequency, V-interruptions and V-unbalance. EN50160 Voltage Magnitude does not list invalid intervals. 

Can you help trouble shoot cause of an invalid interval? 

Thanks.


Accepted Solutions
DanL
Commander Commander
Commander

Re: PM8000 "invalid intervals" for power quality module

"invalid interval" is the (legacy?) EN50160 term for "flagging" a quantity that the signal is so far out of normal bounds that it is not marked as a "failed" interval. For example, an interval with zero voltage will have both frequency and THD marked as "invalid" for the corresponding interval, since it is likely not (just) a frequency or THD issue.

 

The most common problem for this symptom is incorrect meter configuration or wiring.

The meter must be configured for the correct system nominal frequency and nominal voltage.

Of course, if the meter is not properly connected to the configured voltages, intervals will be marked invalid.

 

Other details that help troubleshoot are:
1. "FAC1 Template" version string
2. Nominal Voltage (and actual expected system voltage)
3. PT Prim : PT Sec (if applicable: how many PTs and how are they wired)

4. Volts mode (and which wiring diagram does this installation correspond to)
5. Nominal Frequency (and expected system frequency)

See Answer In Context

3 Replies 3
Charles_Murison
Picard Picard
Picard

CanRe: PM8000 "invalid intervals" for power quality module

 Can you send a screenshot of Vista that includes the title bar with the diagram version?

L4 Prime for Advanced metering and Utilities
DanL
Commander Commander
Commander

Re: PM8000 "invalid intervals" for power quality module

"invalid interval" is the (legacy?) EN50160 term for "flagging" a quantity that the signal is so far out of normal bounds that it is not marked as a "failed" interval. For example, an interval with zero voltage will have both frequency and THD marked as "invalid" for the corresponding interval, since it is likely not (just) a frequency or THD issue.

 

The most common problem for this symptom is incorrect meter configuration or wiring.

The meter must be configured for the correct system nominal frequency and nominal voltage.

Of course, if the meter is not properly connected to the configured voltages, intervals will be marked invalid.

 

Other details that help troubleshoot are:
1. "FAC1 Template" version string
2. Nominal Voltage (and actual expected system voltage)
3. PT Prim : PT Sec (if applicable: how many PTs and how are they wired)

4. Volts mode (and which wiring diagram does this installation correspond to)
5. Nominal Frequency (and expected system frequency)

RdM
Ensign
Ensign
0 Likes
0
725

Re: PM8000 "invalid intervals" for power quality module

Thank you. In our application the meter was correctly configured. 

Your response helped us diagnose that the system being monitored had negligible load while connected pumps weren't running. Therefore, these periods were counted as invalid and reporting was correct.