Good day Team,
Could you please assist with the following issue? We have a PM8000 on site that is failing to connect to ION Setup. The meter is reachable on the network — I am able to ping the device and access the web pages via a browser — however, ION Setup is unable to connect.
Additionally, the firmware version is not displaying on the meter.
Any guidance or troubleshooting steps would be appreciated.
Link copied. Please paste this link to share this article on your social media post.
Hello,
If still having trouble would be good to start a support case with your local technical support or Customer Care team, CCC. If possible would be good to provide a Wireshark packet capture showing communication to the meter with web page and then not communicating to the meter with ION Setup. Would also be good to provide details on how you added the device in ION Setup, single device mode or network mode. If using one I would suggest trying the other as well.
The most likely case is that the port ION Setup is trying to use to talk to the meter is blocked.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
Please ensure that TCP port 7700 is not blocked by the network, as ION Setup uses it to communicate with the meter. e.g, Test-NetConnection -ComputerName IP addr -Port 7700
If possible, try connecting directly to the meter’s ETH1 or ETH2 port, ensuring that both the meter and your PC are on the same subnet.
Are you able to see the meter’s real‑time measured values on the webpage?
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
hi,
yes, i can see real‑time measured values on the webpage.
thank you
Gladwin
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin,
Note that depending on how you are connecting to the meter, single device mode or network mode may also change what port ION setup is trying to use. By default ION Setup will try to use secure ION on port 7443. If ION setup cannot connect on Port 7443, ION Setup will then try 7700.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin ,
Are you still having trouble connecting to the meter?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi, yes, it is currently connected via RS 485 Modbus
Link copied. Please paste this link to share this article on your social media post.
Hello,
If still having trouble would be good to start a support case with your local technical support or Customer Care team, CCC. If possible would be good to provide a Wireshark packet capture showing communication to the meter with web page and then not communicating to the meter with ION Setup. Would also be good to provide details on how you added the device in ION Setup, single device mode or network mode. If using one I would suggest trying the other as well.
The most likely case is that the port ION Setup is trying to use to talk to the meter is blocked.
Regards,
Charles