Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 - TOU 8 tariffs?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 - TOU 8 tariffs?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
195
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Pavel_Melnik
Pavel_Melnik Troubleshooter
Troubleshooter

Posted: ‎2026-05-15 02:15 AM

0 Likes
5
528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-15 02:15 AM

PM8000 - TOU 8 tariffs?

Hi everyone!

One of our customers have a lot of PM8000 meters used on incomers at many sites across the globe.
We are starting to use extensively TOU capabilities to register Active Energy Delivered consumption for different rates like High peak, mid, low. Now customer raises the topic of a configuration of 8 rates for the same day.
According to the specs of PM8000 it is supported:

Pavel_Melnik_0-1778833731767.png

Link to Technical sheet, page 9

Yet, if using ION Setup it is possilble to manage only 4 tariffs:

Pavel_Melnik_2-1778834937797.pngPavel_Melnik_1-1778834829689.png

Same goes when I open the meter with Designer in PME, it just shows one Time of Use modele available with ability to write data into 4 records: A, B, C and D

Pavel_Melnik_3-1778835112804.png


So could anyone please advise me which apporaches are available here to utilize all 8 tarrifs?
Are there any special firmwares or ready-to-use frameworks to import into the meter?

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-05-20 11:54 AM

0 Likes
0
417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-20 11:54 AM

Hello ,

 

In the World of ION there is usually more than 1 way to do things. For example in PME it is possible to setup a TOU that can be customized to a much higher degree than on a meter's TOU module. All the calculations are done after the data is collected. Data logging configuration on the device is default. Benefit of this is, if the rate dates/times change you can make the change once and applies to all reports, would not have to update anything on the device. 

 

If you need calculations done on the device then two TOU modules would be needed. ION can be heavily customized, you could for example use 2 TOU with multiple AND/OR modules to determine multiple rates. The default template only has 4 rates, to add additional rates would require adding additional modules like Sliding Window Demand, and Integrators. Nothing too complex and the existing modules can be used as a template. I do not have examples to provide.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-05-15 10:05 AM

0 Likes
1
502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-15 10:05 AM

Hi @Pavel_Melnik 

 

The TOU Setup Wizard in ION Setup provides configuration for only one TOU module. However, in Advanced mode, it is possible to add a second TOU module, which is the maximum supported. In total, up to 8 TOU rates can be configured, with 4 rates in TOU1 and 4 rates in TOU2.

 

Mehran_Mehrnia_0-1778864638071.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Pavel_Melnik
Pavel_Melnik Troubleshooter
Troubleshooter

Posted: ‎2026-05-16 07:50 AM

0 Likes
0
481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-16 07:50 AM

Hi @Mehran_Mehrnia ,

Yes, I’ve seen that capability. However, it’s still not clear how they are supposed to work together, or whether they can work together at all, to achieve the goal of having 8 different tariffs within a single day.

Besides, simply adding and configuring an additional TOU module through Advanced mode does not automatically create the additional recorders and connections.

So my question still stands.

Reply
Pavel_Melnik
Pavel_Melnik Troubleshooter
Troubleshooter

Posted: ‎2026-05-20 07:41 AM

0 Likes
1
427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-20 07:41 AM

Hi @Charles_Murison ,

I would appreciate to hear your opinion on this one.
By the way, here is an example of 5 rates for one of seasons from July to August.
Is there any proper way to organize it so customer can see the charts in PME with consupmtion from 5 different measurements dedicated to each rate?

Attachments
Example with 5 rates.xlsx
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-05-20 11:54 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-20 11:54 AM

Hello ,

 

In the World of ION there is usually more than 1 way to do things. For example in PME it is possible to setup a TOU that can be customized to a much higher degree than on a meter's TOU module. All the calculations are done after the data is collected. Data logging configuration on the device is default. Benefit of this is, if the rate dates/times change you can make the change once and applies to all reports, would not have to update anything on the device. 

 

If you need calculations done on the device then two TOU modules would be needed. ION can be heavily customized, you could for example use 2 TOU with multiple AND/OR modules to determine multiple rates. The default template only has 4 rates, to add additional rates would require adding additional modules like Sliding Window Demand, and Integrators. Nothing too complex and the existing modules can be used as a template. I do not have examples to provide.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Pavel_Melnik
Pavel_Melnik Troubleshooter
Troubleshooter

Posted: ‎2026-05-20 10:46 PM

0 Likes
0
400
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-20 10:46 PM

Hi @Charles_Murison ,

Thanks for a reply! Ok, I see. Just wanted to make sure I'm not missing existing solution (like a dedicated firmware) or some other straightforward approach.

Yes, we are aware of TOU capabilities in PME, but customer wants to also see the data on the Dashboards and on top of that they want to configure TOU themselves. It was easy to explain how to do it in PME and also in ION Setup for 4 rates but with more rates it gets more complicated and I cannot just simple handle this task to them.

I'm now thinking of using SQL code to determine TOU rates based on the TOU Name, Source and Timestamp in PME. Then I can use it to calculate consumption for each also directly in SQL or using VIP.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore