Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84521members
353751posts

PM8000 Phase order settings

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Koen_Rowies
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
5
642

PM8000 Phase order settings

Hello,

At a customer site i have 2 PM8000 devices with the phasor diagram showing an ACB rotation

When Changing the parameter via the Web interface from ABC to ACB this has no influence on the phasor diagram, shouldn’t this change then to the ABC rotation?

Second question, what happens when this parameter is not correctly set? errors in PME?

Can this parameter also be set in IONsetup? I can't find it there...

Br,

Koen

Tags (2)
5 Replies 5
Bojan
Captain Captain
Captain
0 Likes
0
595

Re: PM8000 Phase order settings

Hi Koen,

I think that Phase Order parameter is suppose to be used in Phase Reversal Unary Alarm detection, but it's not used in PM8000 like in PM5000:

Robert_Lee
Captain Captain
Captain
0 Likes
0
595

Re: PM8000 Phase order settings

The standard ION Setup Assistant does not expose all available registers to most users (in this case, this is a wiring issue which should of been caught during meter installation).  You can view the setup registers by switching into Advanced ION Setup view (Device Properties -> Tools -> Show Advanced Setup) and going into the Power Meter modules and modifying the appropriate setup register.

While you could start swapping polarity registers, we don't recommend this as showing "software" fixed phasors may create safety concerns when servicing the device at a later time.  Another option is you can alter the phasor rotation in ION Setup but this is a global setting which affects all phasor viewers for every device that ION Setup communicates with (Tools -> Options -> Conventions).

Bojan
Captain Captain
Captain
0 Likes
2
595

Re: PM8000 Phase order settings

Hi Koen,

Just a remark that phasing is not standardized across Distribution Systems. For three phase generation, the phase sequence and the direction of rotation must be coordinated with a local  Distribution System.

So, If you see ACB, it doesn't mean that it is a wrong phase rotation.

Best regards,

Bojan

Koen_Rowies
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
595

Re: PM8000 Phase order settings

Hello Bojan,

Indeed this is not always in our hands, the meter is correct wired in the cabinet phase 1, 2, 3 but rotation is different sometimes. I was wondering if the phase rotation parameter has some influence on the alarms in PME. i have changed them but i don't see any difference on alarms...  If it is there it should have some reason...

Br,

Koen

Bojan
Captain Captain
Captain
0 Likes
0
595

Re: PM8000 Phase order settings

Hi Koen,

It would trigger Phase Rotation alarm in PM5000 meter if enabled, but I'm not sure for PME.

PME has configurable Alarms, but the phase rotationerror event has to be triggered by the meter, and I think PM8000 has no such alarm.

Br,

Bojan