PM8000 Digital input scan and count rate

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

daniel_parker_p
Lieutenant
Lieutenant
0 Likes
2
308

PM8000 Digital input scan and count rate

Hi all,

The PM8000 has a default framework for calculating pulse rate and showing the peak rate. What is the maximum rate we can expect out of this in terms of hardware and firmware limitations?

(To put it in context, we want to sample at high speed pulse ~6000kHz and log the count frequency at a much slower speed, maybe 0.5s, do we need to look elsewhere or is there a way we can do this with the PM8000?).

Dan

2 Replies 2
sesa64419
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: PM8000 Digital input scan and count rate

Hi Dan

Looking at the onboard digital input specifications in the PM8000 user manual:

Pulse frequency ≤ 25 Hz

Event timestamp accuracy ± 1 ms

Response time 20 ms

Minimum pulse width 20 ms

Hope this helps,

Alana

daniel_parker_p
Lieutenant
Lieutenant
0 Likes
0
287

Re: PM8000 Digital input scan and count rate

Thanks Alana,

Missed that in the manual, thanks for your help.