As explained in the following FAQ, the meter’s front‑panel display automatically scales voltage, current, and energy readings to the appropriate units. These units cannot be manually changed because they are determined by the configured CT and PT ratios.
In this case, please follow option 2 (or, if possible, option 3) to change the displayed units, as described in this FAQ:
How to Change the Voltage, Current, Power & Energy Units Displayed on ION Meters.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
As explained in the following FAQ, the meter’s front‑panel display automatically scales voltage, current, and energy readings to the appropriate units. These units cannot be manually changed because they are determined by the configured CT and PT ratios.
In this case, please follow option 2 (or, if possible, option 3) to change the displayed units, as described in this FAQ:
How to Change the Voltage, Current, Power & Energy Units Displayed on ION Meters.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.