Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
EL1AKI
EL1AKI Explorer
Explorer
Posted: ‎2026-07-16 01:17 AM
518
Hi team,
Hope you are well.
I am currently working with a customer about their PM8000 to BMS communication.
We recently updated the firmware to V4.6 and enabled the Bacnet protocol.
But not all of the values are being read.
Can you give us some advise what to look at?
Please see attachment.
image001 (8).pngimage002 (1).png Thank you
  • PM8000
Charles_Murison
Champion
Posted: ‎2026-07-16 07:23 AM
1
504
Hello @EL1AKI ,
Not sure if just me but images are too blurry for me to actually see what the issue is. A general troubleshooting would be to check the input to the Data mapping modules are as I believe the meter uses these modules to map the BACnet objects to ION registers.
In ION Setup advanced mode you can hold shift and click on the inputs tap to read the value of inputs. I would suggest checking that the value of inputs match your BACnet values. Note that there are multiple Data mapping modules, you will need to check multiple to find all the BACnet objects.
Charles
Charles_Murison
Champion
1
504
Hello @EL1AKI ,
Charles
EL1AKI
EL1AKI Explorer
Explorer
Posted: ‎2026-07-16 11:54 PM
Hello @Charles_Murison
Thank you, we will double check the inputs first. Will let you know.
Thank you again