Hi @Gladwin
Is the latest firmware version 6.2 running on the meter? As I checked the PM5760 release notes, the latest firmware version is 6.2, but I do not see any fixes related to the behavior you observed, unlike the fix that was provided for the PM5560.
I would recommend opening a ticket for further assistance and investigation with the following information:
Please advise.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
Is the latest firmware version 6.2 running on the meter? As I checked the PM5760 release notes, the latest firmware version is 6.2, but I do not see any fixes related to the behavior you observed, unlike the fix that was provided for the PM5560.
I would recommend opening a ticket for further assistance and investigation with the following information:
Please advise.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
thank you, i will open a ticket
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
You're welcome.
As confirmed by the team, this issue is currently under investigation and will be fixed in the next release.
Further actions will be communicated to you by the support team through the ticket.
Best Regards,
-Mehran
L3 Expert Advanced metering