Dear Team Advance,
I am encountering an issue when configuring the IP address on the Powermeter 5580. Although I enter the correct IP address, it does not update—even after exiting the IP menu, waiting, or power-cycling the unit.
I attempted to use the IP address 169.254.0.10, but it was not detected.
I also tried using IP addresses in the 169.254.XXX.XXX and 85.16.XXX.XXX ranges along with the unit's MAC address, but the result remained the same.
Can this issue be resolved without a firmware upgrade? If so, how? If a firmware upgrade is required, what connection method can be used without an IP address?
I have attached the Powermeter data for your investigation.
Approximately four Powermeters have been found with this same issue.
Link copied. Please paste this link to share this article on your social media post.
Dear @Jesus_Diaz As it happens, I also emailed Advance, and their reply was that the PM unit cannot be repaired and must be replaced with a new one.
Thanks for your Reply.
Link copied. Please paste this link to share this article on your social media post.
Hi @YonKhoerul,
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Dear @Jesus_Diaz As it happens, I also emailed Advance, and their reply was that the PM unit cannot be repaired and must be replaced with a new one.
Thanks for your Reply.