Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
Miyai
Miyai
Contributor
Posted: ‎2026-01-19 09:00 PM
472
In the configuration below, the "In" value is larger than expected.
Do you know why the "In" value is so large?
I output three-phase 50A from the current generator.
At this time, the calculated "In" was assumed to be around 0-1A.
However, the measured value "In" was 70A.
I tried it with multiple PM5560s with the same results.
I have a PM5560 with the following settings:
FW Ver:4.4.9
3P4H Wye Gnd
250/5A
50Hz
I1, I2, I3 setting
(There is no wire connected to the I4 terminal.)
Miyai
  • PM5000
Charles_Murison
Champion
Posted: ‎2026-01-20 10:27 AM
464
Hello @Miyai
A lot will depend on the phase angles of the current as well as the magnitude. In is not calculated on the RMS of the currents. The calculations are a bit more complex.
Charles
Charles_Murison
Champion
464
Hello @Miyai
Charles
Miyai
Miyai
Contributor
Posted: ‎2026-01-20 09:44 PM
Hello @Charles_Murison
Thank you for your advice.
This matter was resolved.
The tester output was incorrect.
The harmonic components had a negative effect.