I2 showing double the amp draw from I1 &I3. Checked with amp meter and all 3 phases running within a few percent. We did have a loose connection on the B phase 125amp main breaker causing it to trip a few times. The breaker was replaced. Also, The middle 100ma fuse was blown for the power management system. Fuse was replaced with correct size and hasn't blown again. All other fuses ok. Compared voltages with another PM5500 system and readings are all similar. Everything else with the PM5500 is ok aside from is just showing an incorrect amp draw on the B phase. Any help would be much appreciated.
Link copied. Please paste this link to share this article on your social media post.
Hi @sbrsa First of all verify configuration and wirings are as per the power system (see instruction sheet: https://download.se.com/files?p_enDocType=Instruction+sheet&p_File_Name=GDE41422-05.pdf&p_Doc_Ref=GD...) . Then, please perform a simple swap test:
Swap CT secondary inputs between I1 & I2 using proper CT safety procedures.
->If the measurement error follows the CT → CT/secondary circuit problem.
->If the error remains on I2 → PM5500 I2 input is likely faulty. Then meter need to be replaced here.
Link copied. Please paste this link to share this article on your social media post.
Hello @sbrsa ,
Some details about the metering missing, the phase angles, system mode, etc. could make a difference.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @sbrsa First of all verify configuration and wirings are as per the power system (see instruction sheet: https://download.se.com/files?p_enDocType=Instruction+sheet&p_File_Name=GDE41422-05.pdf&p_Doc_Ref=GD...) . Then, please perform a simple swap test:
Swap CT secondary inputs between I1 & I2 using proper CT safety procedures.
->If the measurement error follows the CT → CT/secondary circuit problem.
->If the error remains on I2 → PM5500 I2 input is likely faulty. Then meter need to be replaced here.
Link copied. Please paste this link to share this article on your social media post.
Hello @sbrsa ,
In addition to Akash's feedback, please verify the CT rating as well. The same CT rating should be used for all three phases (I1, I2, and I3).
If a different CT rating is used for I2, the device may display an incorrect I2 value, as the device uses a common CT setting for I1, I2, and I3.
Regards,
Rohith S
Link copied. Please paste this link to share this article on your social media post.
Thank you, I will check this out