New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
PM5320 configuration procotols/ports
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2026-02-1801:32 AM
PM5320 configuration procotols/ports
Hi,
I am wondering which protocols and ports the PM5320 uses during configuration using the ION Setup 3.2 and DLF-3000 software. Does the device support the ION protocol w/ TCP 7700, 7443 or is it configured using Modbus TCP 502?
The PM5000 series such as PM5320 is not an ION‑class meter and does not support the ION protocol.
The PM5320 communicates using Modbus TCP on port 502 during configuration (ION Setup 3.2) and firmware upgrades (DLF‑3000). It does not support the ION protocol, therefore neither TCP 7700 nor TLS 7443 are used or available.
The PM5000 series such as PM5320 is not an ION‑class meter and does not support the ION protocol.
The PM5320 communicates using Modbus TCP on port 502 during configuration (ION Setup 3.2) and firmware upgrades (DLF‑3000). It does not support the ION protocol, therefore neither TCP 7700 nor TLS 7443 are used or available.