Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5110 Negative Energy Value

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: PM5110 Negative Energy Value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
solutions_iems-
solutions_iems-
Troubleshooter

Posted: ‎2020-08-10 02:12 AM

0 Likes
2
4801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-10 02:12 AM

PM5110 Negative Energy Value

I have a PM5110 power meter that has decided to change an import energy value into an export energy value.

 

On 12th July at 12:30, the energy reading was 2,147,457.38 kWh

 

Fifteen minutes later at 12:45, the energy reading became -2,147,483.03 kWh, and has stayed a negative value ever since. All kW values have remained positive.

 

The meter serial number is 340060199461 and it is connected to an ION 6.0.1 system using the PM5000 LE 6.0.1.11 driver. I know that the driver is not at fault as the other PM5110 power meters connected to the system are still measuring energy as expected.

 

I have attached a report for this power meter for 12th July 2020.

Attachments
Substation 2_4 Main Incomer 12.07.20.xls
Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-08-10 09:05 AM

1 Like
1
4796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-10 09:05 AM

Hello @solutions_iems- ,

 

‭2147483648‬ is the largest signed integer value for a 32 bit number. If the register is defined as signed, any number larger than this will be considered a negative number in software. Likely there is also scaling involved, possibly 1000. Note that ION Enterprise is very old software and no longer officially supported. You could try looking at the driver to see if possible to change the register to unsigned. 

 

For your data, you would need to find the 2's complement to the number. It is possible the report is rounding/truncating to 2 decimal places. I would look for the value in the database to be sure. for calculate what the energy should be to manually update. New value = ((2^32)/1000 + logged value)

For example -2147456.15 would be 2147511.146

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-08-10 09:05 AM

1 Like
1
4797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-10 09:05 AM

Hello @solutions_iems- ,

 

‭2147483648‬ is the largest signed integer value for a 32 bit number. If the register is defined as signed, any number larger than this will be considered a negative number in software. Likely there is also scaling involved, possibly 1000. Note that ION Enterprise is very old software and no longer officially supported. You could try looking at the driver to see if possible to change the register to unsigned. 

 

For your data, you would need to find the 2's complement to the number. It is possible the report is rounding/truncating to 2 decimal places. I would look for the value in the database to be sure. for calculate what the energy should be to manually update. New value = ((2^32)/1000 + logged value)

For example -2147456.15 would be 2147511.146

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
solutions_iems-
solutions_iems-
Troubleshooter

Posted: ‎2020-08-11 01:51 AM

0 Likes
0
4789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-11 01:51 AM

Hi Charles

 

I should have noticed that the value exceeded the limits of a register format!

 

I have changed the Modbus register for Real Energy into the Load (403204) for the PM5100_LE device driver from S64-87-21 to U64-87-21 format and it has resolved my issue. I will now check the driver types PM5300_LE, PM5350 & PM5500_LE for the same.

 

Thanks

Iain

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore