Greetings guys,
We have potential project with PM2000 and METSEPM2KANLGIO22. And we need to understand a configuration of analog module. Can I put for example negative parameter for lower limit? Because I couldn't test it by myself without physical device in ION setup.
Also, maybe we have some tricks to work with ION setup without physical device?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Hi @HellZet
Yes, you can set negative values for the engineering scale (Lower Limit), but the physical output remains positive such as 4-20mA.
There is no offline device configuration feature in ION Setup for PM2000.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @HellZet
Yes, you can set negative values for the engineering scale (Lower Limit), but the physical output remains positive such as 4-20mA.
There is no offline device configuration feature in ION Setup for PM2000.
Best Regards,
-Mehran
L3 Expert Advanced metering