Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

PCSP HMI does not accept year 2020 in date

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: PCSP HMI does not accept year 2020 in date
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
521
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
134
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-01-06 03:10 AM . Last Modified: ‎2020-12-02 03:31 AM

0 Likes
6
2455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-06 03:10 AM

PCSP HMI does not accept year 2020 in date

Hi Team

 

I have number of PCSP Panels installed which have not updated the date in 2020. It is showing 06/01/2000.

Also could not able to change the date for year 2020.

Please suggest if i have missed out something in settings.

Labels
  • Labels:
  • Power Quality
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-01-08 08:08 PM . Last Modified: ‎2020-03-05 06:28 AM

1 Like
4
2436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 08:08 PM

Hello Team

Good Day

“Wish you All a Very Happy New Year”

We really apologize for the inconvenience.

Issue: As you mentioned, Yes, we have issue with Dates on AccuSine HMI display as year 2000 instead of 2020.

Description: But it affects only the HMI home screen date and time displayed and it will log any events as year 2000 when it occurred in 2020, apart from that this issue does not impact performance or operation of the product.

 

Impact Product Range: All AccuSine PCS+, PFV+ and PCSn in the field.It means all the units that produced before December 31st 2019. Units shipped from Jan 1st, 2020 have the latest FW and are not affected.

No safety, operation or Performance Thread.

Resolution: The fix for this is updating the control board and HMI firmware.  Today this can only be accomplished with the Service Terminal program which is not intended to be released to customers. To avoid having to deploy AccuSine+ trained FSR for this, we are working on a simplified way to deploy the firmware update so a customer can accomplish this task.  Any customers that receive the update to the latest firmware will also have to be told to download the new User Manual (already on se.com).

 

Next step: Until the fix is released, please ask the respective country team to log the complaint in BFO for traceability. A Field Service Bulletin will be issued along with the fix by end-January 2020.

Latest User Manuals released Dec-2019

  • AccuSine PCSP/EVCP user manual

https://schneider-electric.box.com/s/8dzkf5ep2ualyx5v3fhkon9t1t600tji

 

  • AccuSine PCSn user manual

https://schneider-electric.box.com/s/6e8glhf6qppsxxqg1y1qxox5zdxq3c2y

 

Still if you have any questions, let us know.

 

Best Regards

 

Arun

Arunprasad

See Answer In Context

Reply
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-03-05 06:26 AM

2 Likes
1
2398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 06:26 AM

Hi Aaron

 

Yes, issue has been fixed , we have released new firmware for both PCSP and PCSn, you can check with the local service team, they can help you to get the latest version. Official FSB(Field service Bulletin) will be released soon.

Here i am sharing you the link to download the Latest User manual for both PCSP and PCSn, which will help you a lot.

 

  • AccuSine PCSP/EVCP user manual

https://schneider-electric.box.com/s/8dzkf5ep2ualyx5v3fhkon9t1t600tji

 

  • AccuSine PCSn user manual

https://schneider-electric.box.com/s/6e8glhf6qppsxxqg1y1qxox5zdxq3c2y

Arunprasad

See Answer In Context

Reply
Replies 6
Anonymous user
Not applicable

Posted: ‎2020-01-08 10:14 AM . Last Modified: ‎2020-01-10 01:53 AM

0 Likes
5
2443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 10:14 AM

Hi,

 

The community members can you help this member on this topic, please?

 

@Arunprasad or @NicolasLarue  do you think you can advise on this topic?

 

Have a nice day.

Reply
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-01-08 08:08 PM . Last Modified: ‎2020-03-05 06:28 AM

1 Like
4
2437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 08:08 PM

Hello Team

Good Day

“Wish you All a Very Happy New Year”

We really apologize for the inconvenience.

Issue: As you mentioned, Yes, we have issue with Dates on AccuSine HMI display as year 2000 instead of 2020.

Description: But it affects only the HMI home screen date and time displayed and it will log any events as year 2000 when it occurred in 2020, apart from that this issue does not impact performance or operation of the product.

 

Impact Product Range: All AccuSine PCS+, PFV+ and PCSn in the field.It means all the units that produced before December 31st 2019. Units shipped from Jan 1st, 2020 have the latest FW and are not affected.

No safety, operation or Performance Thread.

Resolution: The fix for this is updating the control board and HMI firmware.  Today this can only be accomplished with the Service Terminal program which is not intended to be released to customers. To avoid having to deploy AccuSine+ trained FSR for this, we are working on a simplified way to deploy the firmware update so a customer can accomplish this task.  Any customers that receive the update to the latest firmware will also have to be told to download the new User Manual (already on se.com).

 

Next step: Until the fix is released, please ask the respective country team to log the complaint in BFO for traceability. A Field Service Bulletin will be issued along with the fix by end-January 2020.

Latest User Manuals released Dec-2019

  • AccuSine PCSP/EVCP user manual

https://schneider-electric.box.com/s/8dzkf5ep2ualyx5v3fhkon9t1t600tji

 

  • AccuSine PCSn user manual

https://schneider-electric.box.com/s/6e8glhf6qppsxxqg1y1qxox5zdxq3c2y

 

Still if you have any questions, let us know.

 

Best Regards

 

Arun

Arunprasad
Reply
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-01-10 01:33 AM

1 Like
0
2421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-10 01:33 AM

Hi... Arun

 

Greetings for new year...

 

Thanks for detailed explanation, its going to help us to convince the end user.

 

We will be waiting for the Fix to get released.

 

Thanks to all

Reply
Anonymous user
Not applicable

Posted: ‎2020-03-05 06:18 AM

0 Likes
2
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 06:18 AM

Hi Arun, has the fix been released yet?

 

Also, the links to the latest installation manuals aren't working for me, can you please re-post?

Reply
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2020-03-05 06:26 AM

2 Likes
1
2399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-05 06:26 AM

Hi Aaron

 

Yes, issue has been fixed , we have released new firmware for both PCSP and PCSn, you can check with the local service team, they can help you to get the latest version. Official FSB(Field service Bulletin) will be released soon.

Here i am sharing you the link to download the Latest User manual for both PCSP and PCSn, which will help you a lot.

 

  • AccuSine PCSP/EVCP user manual

https://schneider-electric.box.com/s/8dzkf5ep2ualyx5v3fhkon9t1t600tji

 

  • AccuSine PCSn user manual

https://schneider-electric.box.com/s/6e8glhf6qppsxxqg1y1qxox5zdxq3c2y

Arunprasad
Reply
Anonymous user
Not applicable

Posted: ‎2020-03-12 05:41 PM

1 Like
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-12 05:41 PM

Thanks Arun, appreciated.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore