Hi, I have dual-source switchboard (with ATS).
2 sets of such switchboard.
Each of this switchboard will have VSD hence needing AHF on each side.
Normal condition, each will be fed separately. (inter-tie open)
Ideally, we will size this AHF to cater for "emergency" where single source will feed both switchboards, with inter-tie close.
Do we really need 3 CT measurement points per AHF?
Does it work with our PCS+ (each AHF will need multiple of 200A for e.g. to work in parallel)
If not, any recommendation?
Link copied. Please paste this link to share this article on your social media post.
Hello TC,
Good day!
Yes, you're right, we need 3 CT measurement points per AHF in this scenario.
We recommend you to use summation current transformer which can add multiple CT measurements.
BRs
BRs