Hi, I'm currently involved in a utility-scale PV/BESS project which has an existing Janitza UMG604-PRO installed as the site Point of Connection meter. We have been advised that the existing UMG604-PRO cannot support multiple TCP clients simultaneously where both clients require access at approximately 20 ms polling intervals. I wanted to enquire whether there is a more suitable PQA from the ION range that offers Multiple/Simultaneous Modbus TCP clients Access via a single Ethernet interface High-speed polling in the order of 20 ms Simultaneous access by two PPC/control systems In particular.
Link copied. Please paste this link to share this article on your social media post.
Hello @Mark-Looking4Support ,
ION meters (ION9000, PM8000, ION7400, ION8650) do support multiple Modbus client connections however none of these meters support a polling in the range of 20ms. Communications are a low priority task within the meter so cannot guarantee a response within this time range.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Mark-Looking4Support ,
ION meters (ION9000, PM8000, ION7400, ION8650) do support multiple Modbus client connections however none of these meters support a polling in the range of 20ms. Communications are a low priority task within the meter so cannot guarantee a response within this time range.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
Thank you for your reply and clarification ref ION meters.
Best regards
Mark