Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Modbus Setting EM2357

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Modbus Setting EM2357
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
Power Monitoring Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
AdrianTirta
AdrianTirta
Explorer

Posted: ‎2025-12-03 07:36 PM

0 Likes
6
1217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-03 07:36 PM

Modbus Setting EM2357

Dear Expert,

 

I'm working on a project that uses the EM2357 as the energy meter. I’ve already established communication through the Modbus RS-485 port, with a PAS800L gateway at the end of the daisy chain.

 

My current issue is how to detect and configure each device’s Modbus ID, baud rate, and parity. As you know, the EM2357 does not have a display, so I can't check or modify these parameters directly on the device.

  • Thumbnail of Power Monitoring Expert
    Schneider Electric
    Power Monitoring Expert
View products (1)
Labels
  • Labels:
  • PM Announcements
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2025-12-08 09:32 PM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 09:32 PM

Hi @AdrianTirta I've attached the snap. Please use any Modbus tester software.

akash_das_0-1765258307134.png

 

See Answer In Context

Attachments
Reply
Replies 6
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-12-04 07:49 AM

0 Likes
2
1198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-04 07:49 AM

Hello @AdrianTirta 

Looking at the user guide (EM2357 User guide ) I see the following section:

You can configure the setting parameters of the power meter through the RS-485 communication port
of the power meter.
The default RS-485 communication port setting has been configured when the power meter leaves
the factory. You must modify the default settings before connecting the power meter to the RS-485
network.
RS-485 port setting
The power meter has been configured as the default serial communication settings before leaving the
factory. You need to modify these default settings before connecting the power meter to the RS-485
bus.
The power meter has been configured to use the following default serial communication settings at
the factory:
• Protocol = Modbus RTU
• Address = 1
• Baud rate = 19200
• Data bit = E81 (even parity, 8 data bits, 1 stop bit)

To program this meter you must connect to the meter directly before installing on RS-485 network.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2025-12-07 08:46 PM

0 Likes
2
1153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-07 08:46 PM

Hi @AdrianTirta Please see the attached snap of registers to be used for modification of ID, baud rate & parity. ID can be from 1 to 255, baud rate setting: 0 = 1200,1 = 2400, 2 = 4800, 3 = 9600, 4 = 19200, 5 = 38400 & parity setting: 0 = N81, 1 = E81, 2 = O81, 3 = N82.  Hope this helps!

 

 

Attachments
Reply
AdrianTirta
AdrianTirta
Explorer

Posted: ‎2025-12-08 06:37 AM

0 Likes
1
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 06:37 AM

Hi @akash_das. 

Thank you for your response and for providing the feedback. Unfortunately, I was unable to access the attachment you included, so I could not fully understand your explanation.
Could you kindly resend the attachment?

Reply
AdrianTirta
AdrianTirta
Explorer

Posted: ‎2025-12-08 06:44 AM

0 Likes
1
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 06:44 AM

Hello @Charles_Murison 

Thank you for your response. I understand now that each meter needs to be configured individually before being connected to the RS485 network. However, I would like some clarification on the configuration process.

 

Should I configure the Modbus parameters directly on each device by connecting its RS485 port to my PC (using an RS485-to-USB serial converter), or do I still need to use the PAS800 for this process?

 

Additionally, which software should be used to modify the parameters? Can EPC be used for this purpose, or should I use ION Setup? If there is a specific application required for configuring the EM2357 devices, please let me know.

 

Could you please provide a step-by-step guide starting from how to properly establish the RS485 communication wiring, up to how to modify the Modbus parameters on each device?
I would like to understand the full procedure—whether I need to connect each meter directly to my PC using an RS485-to-USB converter or if the PAS800 is required, and which application should be used for configuration (EPC, ION Setup, or another specific tool).

Thank you.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-12-08 10:05 AM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 10:05 AM

Hello @AdrianTirta ,

 

I do not use the EPC tool so I do not know what devices the software supports. Modbus is a open protocol and there are many different tools that exist that support reading and writing modbus. If you are looking for details instructions I suggest reaching out to your local technical support. 

In general, you connect to the device using Modbus software. There may be specific requirements to write to certain modbus registers, confirm with technical support on any specific instructions. Depending on the devices modbus register list you would write specific values to specific registers to set the configuration of the device. There will be a register for Device ID, one for baud rate and one for serial settings (Data bits, Parity, Stop bits, ex 8N1)

 

I do not have a modbus register list for the device, I suggest to reach out to your local technical support for that information.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
akash_das
akash_das Troubleshooter
Troubleshooter

Posted: ‎2025-12-08 09:32 PM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-08 09:32 PM

Hi @AdrianTirta I've attached the snap. Please use any Modbus tester software.

akash_das_0-1765258307134.png

 

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore