Posted: ‎2026-05-15 07:50 AM
922
Does anyone know why the Circuit Data tab shows the missing voltage (0V) on the channel 1/4/7/...? But the PQM tab shows all voltages just fine. Also verified the voltages on the head unit. The supply type is Delta (3 phases).
FW v0.62.7
  • HDPM6000
Mehran_Mehrnia
Champion
Posted: ‎2026-05-15 10:28 AM
Hi @khanhle
It appears that the voltage reference on Phase 1 is not being transmitted to the branch module over the bus, possibly due to a cable issue. When the branch module’s related channel does not detect the corresponding phase voltage, it will also interpret the associated phase current as zero.
Could you please double-check that the connections and cable are correct?
Best Regards,
-Mehran
L3 Expert Advanced metering
Mehran_Mehrnia
Champion
Hi @khanhle
Best Regards,
-Mehran