Hi everyone,
One of our customers is planning to deploy an ION9000 meter in their facility. They currently have EcoStruxure Power Operation (PO) SCADA running.
The requirement is twofold: they want to integrate the ION9000 into their PO SCADA, and simultaneously read instantaneous power values into an Allen-Bradley PLC.
Here are the specific details and constraints:
PLC Communications: The customer prefers using EtherNet/IP since it's an Allen-Bradley system. However, if EtherNet/IP is not natively supported or recommended for this setup, they are open to using Modbus TCP/IP.
Polling Frequency: The PLC needs to poll the instantaneous power data from the ION9000 at a high frequency—specifically every 100 ms to 200 ms.
What would be the best roadmap or architectural recommendation for this scenario?
Specifically:
Does the ION9000 support native EtherNet/IP, or should we strictly move forward with Modbus TCP/IP for the PLC connection?
Can the ION9000 comfortably handle a 100ms–200ms polling interval from the PLC while simultaneously communicating with Power Operation SCADA without any performance or communication degradation?
Any documentation, whitepapers, or architectural advice on this would be highly appreciated.
Thanks in advancement!
Link copied. Please paste this link to share this article on your social media post.
The ION9000 can support simultaneous communications with Power Operation (PO) and an Allen-Bradley PLC over Ethernet, provided the PLC uses Modbus TCP (or another supported protocol). The ION9000 does not natively support EtherNet/IP.
While the ION9000 supports high-speed Modbus TCP communications, there is no guaranteed Modbus response time or polling rate specification for ION meters. Within the ION architecture, metering, revenue measurements, and power quality functions have higher priority, while communications are a lower-priority task.
As a result, Schneider Electric cannot guarantee deterministic or consistently reliable response times at 100-200 ms polling intervals under all operating conditions, particularly when the meter is busy processing metering, logging, power quality, or other higher-priority functions.
Power Operation and Modbus TCP communications can typically coexist without issue. However, actual performance at high polling rates will depend on factors such as the number of requests, register count, meter workload (logging, power quality events, waveform captures, etc.), concurrent client connections, and network conditions.
There is no specific whitepaper or document that guarantees communication performance at a given polling rate. The recommended references are the ION9000 User Guide(Protocols, ports, and connections), ION Reference, and relevant Schneider Electric FAQs, including guidance on Ethernet communications and supported protocols.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
The ION9000 can support simultaneous communications with Power Operation (PO) and an Allen-Bradley PLC over Ethernet, provided the PLC uses Modbus TCP (or another supported protocol). The ION9000 does not natively support EtherNet/IP.
While the ION9000 supports high-speed Modbus TCP communications, there is no guaranteed Modbus response time or polling rate specification for ION meters. Within the ION architecture, metering, revenue measurements, and power quality functions have higher priority, while communications are a lower-priority task.
As a result, Schneider Electric cannot guarantee deterministic or consistently reliable response times at 100-200 ms polling intervals under all operating conditions, particularly when the meter is busy processing metering, logging, power quality, or other higher-priority functions.
Power Operation and Modbus TCP communications can typically coexist without issue. However, actual performance at high polling rates will depend on factors such as the number of requests, register count, meter workload (logging, power quality events, waveform captures, etc.), concurrent client connections, and network conditions.
There is no specific whitepaper or document that guarantees communication performance at a given polling rate. The recommended references are the ION9000 User Guide(Protocols, ports, and connections), ION Reference, and relevant Schneider Electric FAQs, including guidance on Ethernet communications and supported protocols.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi Mehran,
Thank you for the clear and detailed explanation.
This fully answers our questions. We now have a solid understanding of the communication priorities within the ION architecture and why a 100–200 ms polling interval cannot be guaranteed under heavy meter workloads.
We will proceed with Modbus TCP and guide the customer on adjusting their PLC polling expectations and architecture accordingly.
Thanks again for your support!