Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Integration of ION9000 with Power Operation (PO) and Allen-Bradley PLC via EtherNet/IP or Modbus TCP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Integration of ION9000 with Power Operation (PO) and Allen-Bradley PLC via EtherNet/IP or Modbus TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Caglar_Abatay
Caglar_Abatay Mentor
Mentor

Posted: ‎2026-07-20 04:56 AM

0 Likes
2
548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-20 04:56 AM

Integration of ION9000 with Power Operation (PO) and Allen-Bradley PLC via EtherNet/IP or Modbus TCP

Hi everyone,

One of our customers is planning to deploy an ION9000 meter in their facility. They currently have EcoStruxure Power Operation (PO) SCADA running.

The requirement is twofold: they want to integrate the ION9000 into their PO SCADA, and simultaneously read instantaneous power values into an Allen-Bradley PLC.

Here are the specific details and constraints:

  1. PLC Communications: The customer prefers using EtherNet/IP since it's an Allen-Bradley system. However, if EtherNet/IP is not natively supported or recommended for this setup, they are open to using Modbus TCP/IP.

  2. Polling Frequency: The PLC needs to poll the instantaneous power data from the ION9000 at a high frequency—specifically every 100 ms to 200 ms.

What would be the best roadmap or architectural recommendation for this scenario?

Specifically:

  • Does the ION9000 support native EtherNet/IP, or should we strictly move forward with Modbus TCP/IP for the PLC connection?

  • Can the ION9000 comfortably handle a 100ms–200ms polling interval from the PLC while simultaneously communicating with Power Operation SCADA without any performance or communication degradation?

Any documentation, whitepapers, or architectural advice on this would be highly appreciated.

Thanks in advancement!

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-20 07:46 AM

1 Like
1
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-20 07:46 AM

Hi @Caglar_Abatay 

 

 

The ION9000 can support simultaneous communications with Power Operation (PO) and an Allen-Bradley PLC over Ethernet, provided the PLC uses Modbus TCP (or another supported protocol). The ION9000 does not natively support EtherNet/IP.

 

While the ION9000 supports high-speed Modbus TCP communications, there is no guaranteed Modbus response time or polling rate specification for ION meters. Within the ION architecture, metering, revenue measurements, and power quality functions have higher priority, while communications are a lower-priority task.

As a result, Schneider Electric cannot guarantee deterministic or consistently reliable response times at 100-200 ms polling intervals under all operating conditions, particularly when the meter is busy processing metering, logging, power quality, or other higher-priority functions.

 

Power Operation and Modbus TCP communications can typically coexist without issue. However, actual performance at high polling rates will depend on factors such as the number of requests, register count, meter workload (logging, power quality events, waveform captures, etc.), concurrent client connections, and network conditions.

 

There is no specific whitepaper or document that guarantees communication performance at a given polling rate. The recommended references are the ION9000 User Guide(Protocols, ports, and connections), ION Reference, and relevant Schneider Electric FAQs, including guidance on Ethernet communications and supported protocols.


Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-07-20 07:46 AM

1 Like
1
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-20 07:46 AM

Hi @Caglar_Abatay 

 

 

The ION9000 can support simultaneous communications with Power Operation (PO) and an Allen-Bradley PLC over Ethernet, provided the PLC uses Modbus TCP (or another supported protocol). The ION9000 does not natively support EtherNet/IP.

 

While the ION9000 supports high-speed Modbus TCP communications, there is no guaranteed Modbus response time or polling rate specification for ION meters. Within the ION architecture, metering, revenue measurements, and power quality functions have higher priority, while communications are a lower-priority task.

As a result, Schneider Electric cannot guarantee deterministic or consistently reliable response times at 100-200 ms polling intervals under all operating conditions, particularly when the meter is busy processing metering, logging, power quality, or other higher-priority functions.

 

Power Operation and Modbus TCP communications can typically coexist without issue. However, actual performance at high polling rates will depend on factors such as the number of requests, register count, meter workload (logging, power quality events, waveform captures, etc.), concurrent client connections, and network conditions.

 

There is no specific whitepaper or document that guarantees communication performance at a given polling rate. The recommended references are the ION9000 User Guide(Protocols, ports, and connections), ION Reference, and relevant Schneider Electric FAQs, including guidance on Ethernet communications and supported protocols.


Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Caglar_Abatay
Caglar_Abatay Mentor
Mentor

Posted: ‎2026-07-21 04:40 AM

0 Likes
0
517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-07-21 04:40 AM

Hi Mehran,

Thank you for the clear and detailed explanation.

This fully answers our questions. We now have a solid understanding of the communication priorities within the ION architecture and why a 100–200 ms polling interval cannot be guaranteed under heavy meter workloads.

We will proceed with Modbus TCP and guide the customer on adjusting their PLC polling expectations and architecture accordingly.

Thanks again for your support!

Best regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore