Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 showing correct MW per phase but total kW and kWh not accumulating properly

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 showing correct MW per phase but total kW and kWh not accumulating properly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
MIKEEECHAN
MIKEEECHAN
Explorer

Posted: ‎2026-04-01 07:55 AM

0 Likes
2
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-01 07:55 AM

ION9000 showing correct MW per phase but total kW and kWh not accumulating properly

Hi everyone,
I’m currently troubleshooting a Schneider PowerLogic ION9000 meter and encountered an issue with power and energy calculations.
Current observations:
Per-phase power readings are correct:
Phase A ≈ 5.1 MW
Phase B ≈ 5.3 MW
Phase C ≈ 5.2 MW
Total power should be around 15–16 MW
However:
Some total power displays previously showed near zero
Now total kW is visible (~15.8 MW), but:
kWh is barely incrementing (e.g., +0.001 kWh only)
Energy values (kWh/kVAh) are not accumulating as expected
Additional info:
Metering setup:
3W4W WYE
CT ratio: 600/5
PT ratio: 20125/115
Phasor diagram looks correct (no obvious polarity inversion)
Energy Applications and Incremental Energy appear disabled or not configured
No recent DCF/template reload has been performed
Concern:
At ~15 MW load, energy should increase significantly (hundreds of kWh per minute), but current behavior does not match expected values.
Question:
Has anyone encountered this issue where:
Instantaneous power is correct
But total energy (kWh) is not integrating properly?
Could this be due to:
Missing or corrupted energy integrator module?
Incorrect register mapping?
Template/configuration issue?
Any guidance on where to check or how to restore proper energy accumulation would be greatly appreciated.
Thanks in advance!

Attachments
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-04-02 09:31 AM

1 Like
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-02 09:31 AM

Hello @MIKEEECHAN ,

 

If you meter does not have any custom framework elements, you can try re-paste the template on the meter.  

If you do have customer elements, you may want to confirm the desired outputs of external Boolean modules.

 

Likely your meter is currently using metering units for total power and PT/CT ratios for the individual phases. There are settings configured by the external Boolean modules to tell the meter to apply or not apply scaling to total power readings.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-02 09:12 AM . Last Modified: ‎2026-04-02 10:23 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-02 09:12 AM

Hi @MIKEEECHAN 

 

The Volts Mode is either:

4W-WYE

or

3W-WYE which is a very specific use case, and should only be used in systems (with two PTs measuring two out of three phases) referenced to Neutral where the system is assumed to be perfectly balanced which is often not the case at customer sites.

 

I would double-check the Phasor Diagram to confirm the wiring and phase rotation, especially when the total power does not align with the per-phase power as shown in the attached images, even though you mentioned the total power now appears correct.

As a starting point, please review the Power Meter module and the related Integrator module output registers in Advanced mode of ION Setup. Hold the Control key while selecting the meter to access the advanced view and verify the live values.

Mehran_Mehrnia_0-1775143720479.png

Mehran_Mehrnia_1-1775145811202.png


Following Charles’s advice in the next post, one of the External Boolean modules that can also be checked in the Setup Assistant is 'Scale Rev Param', which specifies whether the revenue readings are presented as primary-side or secondary-side values:

Mehran_Mehrnia_0-1775150540559.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-04-02 09:31 AM

1 Like
0
1050
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-02 09:31 AM

Hello @MIKEEECHAN ,

 

If you meter does not have any custom framework elements, you can try re-paste the template on the meter.  

If you do have customer elements, you may want to confirm the desired outputs of external Boolean modules.

 

Likely your meter is currently using metering units for total power and PT/CT ratios for the individual phases. There are settings configured by the external Boolean modules to tell the meter to apply or not apply scaling to total power readings.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore