Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 SubSynchronous Oscillation mapping

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 SubSynchronous Oscillation mapping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
575
Mehran_Mehrnia
Mehran_Mehrnia Champion
214
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
SESA161069_EF33
SESA161069_EF33 Troubleshooter
Troubleshooter

Posted: ‎2026-09-17 05:29 AM

0 Likes
2
108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-17 05:29 AM

ION9000 SubSynchronous Oscillation mapping

Hello,

 

in ION9000, can the SubSynchronous Oscillation detection signal be mapped on an IEC61860 Goose signal or on a IEC61850 MMS signal ?
If not, on which communication protocol can it be mapped ?

In addition, where are accessible the IEC61850 PICS, MICS, PIXIT, TICS file ?

 

Best regards

Eric FIERFOL
Energy Business Automation COE
Lattes France
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-17 08:13 AM . Last Modified: ‎2026-09-17 08:14 AM

2 Likes
1
99
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-17 08:13 AM

Hi @SESA161069_EF33 

 

The ION9000 does not support IEC 61850 GOOSE messaging, so the Subsynchronous Oscillation (SSO) detection/status signal cannot be published as a GOOSE message.

 

The ION9000 does, however, support IEC 61850 client/server communication as an IEC 61850 IED/server. This communication uses MMS (Manufacturing Message Specification) for client/server data exchange.

 

SSO information that is available as an ION register can potentially be exposed through IEC 61850 using the meter's custom GGIO modules, depending on the type of SSO output required:

  • Numeric SSO values can be mapped through the IEC 61850 GGIO Custom Analog module, which allows up to 16 user-selected numeric ION registers to be made available as IEC 61850 analog values.
  • Boolean SSO detection/alarm signals, if available or created as Boolean ION registers, can be mapped through the IEC 61850 GGIO Custom Digital module, which supports up to 16 Boolean ION registers.


The resulting communication path would therefore be:

SSO ION register → IEC 61850 GGIO → IEC 61850 client/server (MMS) → SCADA/IEC 61850 client

 

If IEC 61850 is not the desired method, Modbus TCP and DNP3 are also supported alternatives on the ION9000.

 

For DNP3, the ION9000 operates as a DNP slave/outstation, and its DNP map can be customized. The DNP Slave Export module can map an ION register to a DNP point for retrieval by a DNP master. Numeric values can be exposed as DNP Analog Inputs, while Boolean values can be exposed as Binary Inputs.

 

Therefore, the available approaches are:

  • IEC 61850 GOOSE: Not supported
  • IEC 61850 client/server (MMS): Supported, with custom GGIO mapping available
  • DNP3: Supported, with configurable ION-to-DNP mapping
  • Modbus TCP: Supported, with configurable mapping


Regarding the IEC 61850 PICS, MICS, PIXIT and TICS files, for the ION meters such as ION9000, IEC 61850 configuration and implementation information is provided primarily through the IEC 61850 and ION Technology documentation, the ION Reference, and the applicable ICD/CID files for implementation and configuration information.

 

The ION9000 firmware package provides the applicable ICD file, which is used with CET850 to build the CID file that is loaded into the meter to enable IEC 61850 functionality.

 

Best Regards,

-Mehran
L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-09-17 08:13 AM . Last Modified: ‎2026-09-17 08:14 AM

2 Likes
1
100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-17 08:13 AM

Hi @SESA161069_EF33 

 

The ION9000 does not support IEC 61850 GOOSE messaging, so the Subsynchronous Oscillation (SSO) detection/status signal cannot be published as a GOOSE message.

 

The ION9000 does, however, support IEC 61850 client/server communication as an IEC 61850 IED/server. This communication uses MMS (Manufacturing Message Specification) for client/server data exchange.

 

SSO information that is available as an ION register can potentially be exposed through IEC 61850 using the meter's custom GGIO modules, depending on the type of SSO output required:

  • Numeric SSO values can be mapped through the IEC 61850 GGIO Custom Analog module, which allows up to 16 user-selected numeric ION registers to be made available as IEC 61850 analog values.
  • Boolean SSO detection/alarm signals, if available or created as Boolean ION registers, can be mapped through the IEC 61850 GGIO Custom Digital module, which supports up to 16 Boolean ION registers.


The resulting communication path would therefore be:

SSO ION register → IEC 61850 GGIO → IEC 61850 client/server (MMS) → SCADA/IEC 61850 client

 

If IEC 61850 is not the desired method, Modbus TCP and DNP3 are also supported alternatives on the ION9000.

 

For DNP3, the ION9000 operates as a DNP slave/outstation, and its DNP map can be customized. The DNP Slave Export module can map an ION register to a DNP point for retrieval by a DNP master. Numeric values can be exposed as DNP Analog Inputs, while Boolean values can be exposed as Binary Inputs.

 

Therefore, the available approaches are:

  • IEC 61850 GOOSE: Not supported
  • IEC 61850 client/server (MMS): Supported, with custom GGIO mapping available
  • DNP3: Supported, with configurable ION-to-DNP mapping
  • Modbus TCP: Supported, with configurable mapping


Regarding the IEC 61850 PICS, MICS, PIXIT and TICS files, for the ION meters such as ION9000, IEC 61850 configuration and implementation information is provided primarily through the IEC 61850 and ION Technology documentation, the ION Reference, and the applicable ICD/CID files for implementation and configuration information.

 

The ION9000 firmware package provides the applicable ICD file, which is used with CET850 to build the CID file that is loaded into the meter to enable IEC 61850 functionality.

 

Best Regards,

-Mehran
L3 Expert Advanced metering

Reply
SESA161069_EF33
SESA161069_EF33 Troubleshooter
Troubleshooter

Posted: ‎2026-09-18 01:37 AM

0 Likes
0
81
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-09-18 01:37 AM

Thanks Mehran 

 

very clear.

Eric FIERFOL
Energy Business Automation COE
Lattes France
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore