Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

【ION9000,PM8000】Wiring connection for 1PH2W

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【ION9000,PM8000】Wiring connection for 1PH2W
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Miyai
Contributor

Posted: ‎2025-12-16 04:51 PM

0 Likes
2
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-16 04:51 PM

【ION9000,PM8000】Wiring connection for 1PH2W

Hello,

 

I have received below inquiry from a customer and would like some advice.

 

Is 1PH2W connection diagram in the installation manual correct?
When I tried this wiring, a sag alarm was constantly detected and the voltage could not be properly monitored.

 

Voltage mode is set to single.
In case of a single setting, Vn is thought of as L-N voltage.

 

When I checked the voltage of L2-V, it was 0V, so I think a sag is being detected all the time.

 

Therefore, I am considering changing to the red line wiring method, but will this have any adverse effects on the measurement information?
For example, calculations such as power and THD.

 

Miyai_0-1765932626102.png

 

 

 

Best regards,

Miyai

Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-12-16 05:34 PM . Last Modified: ‎2025-12-16 05:35 PM

1 Like
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-16 05:34 PM

Hi @Miyai 

 

If Volts mode is set to SINGLE, meter will monitor line to neutral signals of both Vln a and Vln b:

ION Reference -> Sag/Swell Module:

Mehran_Mehrnia_1-1765934411824.png

 

In this case, when meter is wired as 1 phase with Volts mode as SINGLE and 1PH2W LL:

Mehran_Mehrnia_2-1765935090815.png

meter will be in constant Sag/Swell detection mode, cause in SINGLE mode, the Sag/Swell module only processes and updates V1 and V2 and since V2=VN=0, it will trigger the Sag/Swell module.

 

As stated in a similar forum: ION 9000 single phase wiring

"If your wiring doesn't have the V2 terminal connected to a signal, then(in Advanced mode of ION Setup) simply re-link the inputs of the SagSwell module such that the SagSwell V2 input is linked to the same source output as the V1 input ("PQA VLN1 Half Cycle"). This will allow the module to function properly in Single Phase volts mode."

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-12-16 05:34 PM . Last Modified: ‎2025-12-16 05:35 PM

1 Like
0
712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-16 05:34 PM

Hi @Miyai 

 

If Volts mode is set to SINGLE, meter will monitor line to neutral signals of both Vln a and Vln b:

ION Reference -> Sag/Swell Module:

Mehran_Mehrnia_1-1765934411824.png

 

In this case, when meter is wired as 1 phase with Volts mode as SINGLE and 1PH2W LL:

Mehran_Mehrnia_2-1765935090815.png

meter will be in constant Sag/Swell detection mode, cause in SINGLE mode, the Sag/Swell module only processes and updates V1 and V2 and since V2=VN=0, it will trigger the Sag/Swell module.

 

As stated in a similar forum: ION 9000 single phase wiring

"If your wiring doesn't have the V2 terminal connected to a signal, then(in Advanced mode of ION Setup) simply re-link the inputs of the SagSwell module such that the SagSwell V2 input is linked to the same source output as the V1 input ("PQA VLN1 Half Cycle"). This will allow the module to function properly in Single Phase volts mode."

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Miyai
Miyai
Contributor

Posted: ‎2025-12-16 05:52 PM

0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-12-16 05:52 PM

Hi @Mehran_Mehrnia 

 

Thank you for your support.
I understand your solution.

 

However, I feel this is a difficult issue for a first-time customer to deal with.
I'll consider how to respond.

 

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore