Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 Modbus issues

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Modbus issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Gladwin
Gladwin Contributor
Contributor

Posted: ‎2026-04-09 12:41 AM

0 Likes
2
498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-09 12:41 AM

ION9000 Modbus issues

Hi Team,

When the Modbus TCP connection is established with the meter on port 502, the connection is successful.
However, once a data poll is initiated, the response times out and the meter immediately closes the connection on port 502.

As a last resort, I attempted updating the firmware to the latest version, but this did not resolve the Modbus TCP communication issue.

 

can please advise on this 

Gladwin 

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-09 09:18 AM

0 Likes
0
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-09 09:18 AM

Hi @Gladwin 

 

 

 

Here are the possibilities I recommend verifying:

  • Modbus TCP Timeout: Check the Modbus TCP Idle Timeout; this is the number of seconds the meter maintains a connection after it becomes idle. Note that a setting of 0 disables the timeout feature.

  • Security Settings: In the security settings, ensure Modbus Map Access is not set to 'None'. If this parameter is set to 'None,' the meter may return an 'Illegal Data Address' error or reset the connection.

  • Unit ID: Verify the Unit ID (Slave ID). If the Modbus Gateway is enabled, the preferred Unit ID is typically 255.

  • Protocol Status: Confirm that Modbus TCP is explicitly enabled on the port.

  • Register Range: Invalid Register Requests: Ensure your software isn't polling a range that doesn't exist.

  • Network Interference: Firewall/IPS Interference: An intermediate switch or firewall might identify the Modbus 'Read' command as a threat and terminate the TCP stream.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-04-09 09:18 AM

0 Likes
0
485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-09 09:18 AM

Hi @Gladwin 

 

 

 

Here are the possibilities I recommend verifying:

  • Modbus TCP Timeout: Check the Modbus TCP Idle Timeout; this is the number of seconds the meter maintains a connection after it becomes idle. Note that a setting of 0 disables the timeout feature.

  • Security Settings: In the security settings, ensure Modbus Map Access is not set to 'None'. If this parameter is set to 'None,' the meter may return an 'Illegal Data Address' error or reset the connection.

  • Unit ID: Verify the Unit ID (Slave ID). If the Modbus Gateway is enabled, the preferred Unit ID is typically 255.

  • Protocol Status: Confirm that Modbus TCP is explicitly enabled on the port.

  • Register Range: Invalid Register Requests: Ensure your software isn't polling a range that doesn't exist.

  • Network Interference: Firewall/IPS Interference: An intermediate switch or firewall might identify the Modbus 'Read' command as a threat and terminate the TCP stream.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Gladwin
Gladwin Contributor
Contributor

Posted: ‎2026-04-15 05:59 AM

0 Likes
0
397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-04-15 05:59 AM

hi, thank you this worked 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore