ION9000 Logging two sources
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Re: ION9000 Logging two sources
Charles_Murison
Charles_Murison Champion
572
Mehran_Mehrnia
Mehran_Mehrnia Champion
209
Ramasamy_N
Ramasamy_N Champion
115
Anonymous user
Not applicable
Posted: ‎2020-03-05 02:59 AM
1996
Is there an effective way of logging energy usage and power on an ION9000 from two different sources ?
Situation is that we have a site with a generator and mains incoming supply both upstream of the ION9000 with one set of CT's and Vrefs, can we give a digital input to the meter and have it log energy or other measurement to a different register so we can report in PME on just generator usage ?
Layout like this:
Mains    Gen
   X           X         ION
    ---------------------0------->
Anybody done anything like this and care to share the process ?
Charles_Murison
Champion
Posted: ‎2020-03-06 10:41 AM
Hello Grant,
Many of the alarms come from set point modules, these modules have an Enable input. You could link the enable input to the Digital input state.
Charles
Replies 4
Charles_Murison
Champion
Posted: ‎2020-03-05 09:08 AM
Hello Rich,
The digital input can be linked to the enable of the integrator module, you would be able to turn energy accumulation on and off using the digital input. This could be applied to integrators for the main and generator. Sliding Window demand can also be setup like this as well as data recorders. Depending on what measurements you want you can likely do this.
Charles
DanL
DanL Champion
Champion
Posted: ‎2020-03-05 01:32 PM
2
1980
Have a look at the Conditional Energy feature in the default template
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=ConditionalEnergy-5546D2B4...
Grant_IPACS
Grant_IPACS
Mentor
Posted: ‎2020-03-05 09:29 PM
1976
Wondering if i can apply this to a circuit for monitoring generator circuit only... as it is normally zero... maybe halt logging while gen not running, as meter currently logs many errors when generator is off... can we suppress alarms such as low volt, when say DI1 (Gen run) input is off?
Grant
Charles_Murison
Champion
Hello Grant,
Charles
