Hi There,
We have an ION9000 meter in the field that experienced a strange issue with one of its External Pulse modules.
It was noted that the External Pulse module appeared to be periodically pulsing itself for an extended period of time, almost exactly every 5 seconds for over a day, after some testing was done by writing to the External Pulse module from PME.
Looking in the event log of the meter it appeared to be a control action using the ION meter credentials, which ruled out a Modbus source.
The External Pulse module was linked to PME vista graphics, but no manual action was being taken to perform the pulse action over this period.
Upon deleting the External Pulse module and replacing it with a new External Pulse module with the same number (EP45), the module stopped pulsing, which ruled out any external system writing to the External Pulse module.
Screenshot of the event log below, showing the External Pulse module being written to seemingly caught in a 5 second loop by itself.
Is there any known issue or interaction with ION9000 firmware 4.5.0 and/or PME 2023 that could explain this strange External Pulse module behavior?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
As an update we have found the source of the issue. There was indeed a distributed pulse module hidden away in the VIP created via a copy / paste error.
The Meter external pulse was triggering the VIP distributed pulse which was in turn triggering the meter external pulse over and over again in a loop.
When EP45 was deleted, it did not exist to receive the VIP distributed pulse, and so the looping stopped. When EP45 was recreated the issue appeared fixed because the looping had stopped, but it restarted as soon as EP45 was pulsed.
The VIP distributed pulse module has been removed and therefore the issue is resolved.
Link copied. Please paste this link to share this article on your social media post.
Hello @CamboHeath ,
I do not know of any known issue that would cause the meter to start triggering the External pulse by itself. The screenshot posted shows the module created then the pulsing started. I do not see the module getting deleted in the event log and recreated.
Did you confirm that there is nothing in the VIP linked to the external pulse of the meter?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
Thanks for the reply.
The first line in the event log is me creating a new External Pulse module (EP 49) to see if i could replicate the issue, which I could not. This is a different External Pulse module to the External Pulse module experiencing the issue (EP45).
The second line in the event log is me setting the priority of EP45 to 127 so that I could see what was happening in the meters event log, with the subsequent entries in the event log indeed showing a periodic control action being written to the module every 5 seconds, but from a unknown source.
I did not include a screenshot of the deletion and recreation of the module in question (EP45), but the erroneous behavior ceased when this action was undertaken.
The External Pulse module does not allow inputs to be linked to it, so to my understanding it is not possible to trigger an external pulse via ION except for a distributed pulse module, or manual interaction like with a trigger on the PME graphics or manually within the module setup window in designer.
I will do some more investigation on my end, just wanted to check if this was a known issue which it sounds like it is not.
Thanks Charles
Link copied. Please paste this link to share this article on your social media post.
As an update we have found the source of the issue. There was indeed a distributed pulse module hidden away in the VIP created via a copy / paste error.
The Meter external pulse was triggering the VIP distributed pulse which was in turn triggering the meter external pulse over and over again in a loop.
When EP45 was deleted, it did not exist to receive the VIP distributed pulse, and so the looping stopped. When EP45 was recreated the issue appeared fixed because the looping had stopped, but it restarted as soon as EP45 was pulsed.
The VIP distributed pulse module has been removed and therefore the issue is resolved.