Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 read Device Type and Serial Number over Modbus

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 read Device Type and Serial Number over Modbus
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
195
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
simar
simar
Explorer

Posted: ‎2026-03-23 09:31 AM

0 Likes
5
868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-23 09:31 AM

ION8650 read Device Type and Serial Number over Modbus

Hi
Is there a way to make it possible to readout

  • Device Type (FAC1 DeviceType)
  • Serial Number (FAC1 SerialNum)
  • Revision (FAC1 Revision, (optionally))

via Modbus on an ION8650 power meter?

ION8650_desired.png


I have tried to map these information to modbus registers via ION Setup (follow my way in the image), but they do not seem to be available in the Factory Modules.

ION8650_unavailable.png

 

Background: I need to check whether the device my modbus master device is talking to is actually an ION8650 meter and to exactly identify the device via serial number.

ION Setup is version 3.2.25317.02

Thank you in advance, simar

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-03-30 02:06 PM

0 Likes
0
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-30 02:06 PM

Hello  

1) Correct, with default modbus configuration ION8650 meters with V4.40.1 firmware, do not include way to identify meter. In the world of ION many things are possible. For example, the PT primary and  PT secondary can be set to a range of numbers as long as the ratio stays the say. If meter is direct connect, you could set PT Primary and PT secondary to the last 3 numbers in the serial. If you need PT ratios that are quite large, you may not be able to do a trick like this. 

 

2) Locking has a specific meaning in the world of ION8650 meters. The meters could be revenue locked that prevent making changes to any parameter that could affect revenue billing (power and energy etc.). The options string does not suggest that this is the case. If you have a user and password that is able to write to the meter it is possible to create the External numeric module (not external to the meter) with software. 

3) DLMS will not give you real time readings, only logged data. DNP3.0 I do not see any mention of serial number in the Device profile document. https://download.schneider-electric.com/files?p_Doc_Ref=70022-0126-00&p_enDocType=User+guide&p_File_...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Jesus_Diaz
Jesus_Diaz Mentor
Mentor

Posted: ‎2026-03-24 07:26 AM

2 Likes
3
862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-24 07:26 AM

Hi @simar,

 

In the ION8650, starting from firmware version V004.xxx.xxx, the default Modbus registers no longer provide the model number. There is no default register available to retrieve the device type. However, it is possible to modify the meter’s Modbus register list and map an External Numeric (with the defined device‑type value) to a new custom register. To create an External Numeric module, you need to access Advanced Mode in ION Setup (press Ctrl + click on the meter).

 

The firmware version is provided as ASCII characters in registers 1901 to 1912.

 

Regards,

JD

Attachments
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-03-24 09:25 AM

2 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-24 09:25 AM

To extend what Jesus is talking about, you can use multiple external numeric modules to create a series of registers that could then be read by software and understood to me ASCII.
For Example a serial number MW-0901B123-01, convert this into a series of ASCII values, M = 0x4D, W=0x57 '0'=0x30 .... Combine pairs of characters, 'MW' = 0x4D57 = 19799, '09' = 0x3039 = 12345  ... continue until you have the serial number as desired. If you are okay with not including the letters you could simplify the serial number to just the 0901, and 123 as external numeric registers. The letter between 0901 and 123 could also be read as a thousand A=0,B=1,C=2 ... Then 2 external numeric numbers could be 901 and 1123.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
simar
simar
Explorer

Posted: ‎2026-03-26 05:48 AM

0 Likes
1
770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-26 05:48 AM

Hi @Jesus_Diaz 

 

Thank you for your detailed explanation!

I was able to successfully read the firmware version.

 

I do have a couple of follow-up questions to clarify my understanding:

  1. Am I correct in understanding that, with the default Modbus configuration, there is no way to identify whether my Modbus master is connected to a Schneider Electric device (e.g., an ION8650), nor to retrieve details such as the device model or serial number?

  2. Regarding the creation of an External Numeric module in ION Setup: does this require physically unlocking the meter (i.e., opening the device), or can it be done purely through software access?

  3. In the end, I want to read energy and power data from the meter, but I must identify the device first. Initially, I considered modbus to be the simplest solution. However, if the meter cannot be identified over modbus, is another protocol supported by the ION8650 (e.g. DLMS or DNP V3.00) maybe more suitable to this problem? Ideally, no modifications should be necessary on the meter (exept settings than can be made with the buttons on the device itself or via the used protocol) to read power / energy data and device identification information.

Kind regards,
Simar

Reply
Jesus_Diaz
Jesus_Diaz Mentor
Mentor

Posted: ‎2026-03-30 01:49 PM

0 Likes
0
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-30 01:49 PM

Hi @simar,

 

  1. No, not with the default template.
  2. You can access and program the meter using ION Setup by connecting to the meter over Ethernet.
  3. I’m not sure if DNP3.0 will help. @Charles_Murison, do you know if DNP3.0 or any other protocol can identify the meter without modifications?
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-03-30 02:06 PM

0 Likes
0
760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-30 02:06 PM

Hello  

1) Correct, with default modbus configuration ION8650 meters with V4.40.1 firmware, do not include way to identify meter. In the world of ION many things are possible. For example, the PT primary and  PT secondary can be set to a range of numbers as long as the ratio stays the say. If meter is direct connect, you could set PT Primary and PT secondary to the last 3 numbers in the serial. If you need PT ratios that are quite large, you may not be able to do a trick like this. 

 

2) Locking has a specific meaning in the world of ION8650 meters. The meters could be revenue locked that prevent making changes to any parameter that could affect revenue billing (power and energy etc.). The options string does not suggest that this is the case. If you have a user and password that is able to write to the meter it is possible to create the External numeric module (not external to the meter) with software. 

3) DLMS will not give you real time readings, only logged data. DNP3.0 I do not see any mention of serial number in the Device profile document. https://download.schneider-electric.com/files?p_Doc_Ref=70022-0126-00&p_enDocType=User+guide&p_File_...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore