Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 - kWh delivery data stuck

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 - kWh delivery data stuck
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
TJ22
TJ22
Explorer

Posted: ‎2026-01-13 07:36 PM

0 Likes
5
488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-13 07:36 PM

ION8650 - kWh delivery data stuck

Hello there & good morning,


My name is Teja, I have an issue with the ION8650, where the kWh delivery data displayed on the RTU HMI is halt. The factual conditions in the field are as follows:

  1. The kWh delivery value on the RTU HMI is not changing and is stuck at 2147483647 kWh.

  2. Other parameters are operating normally.

  3. The kWh delivery value on the ION8650 meter itself is normal; the data can be downloaded manually and matches the meter reading.

  4. There have been no changes to the RTU configuration.

  5. The ION8650 meter was checked using IEDScout to verify IEC 61850 communication from the meter to the RTU → the kWh delivery data is halt, while other parameters are normal.

I would like to ask whether you have encountered a similar case and what the recommended troubleshooting steps would be.

I have checked the ION8650 settings, and the only related parameter I found is data rollover. There is no configuration related to a data range limit that could cause the value to be held or freeze.

 

Thank you very much for your support.

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-01-14 09:04 AM . Last Modified: ‎2026-01-14 09:13 AM

0 Likes
1
483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-14 09:04 AM

Hi @TJ22 

 

I believe this is related to IEC 61850 editions each meter's firmware and model supports.

 

The kWh delivery value stopped updating because the IEC 61850 configuration used Edition 1, where TotWh.actVal is defined as INT32. INT32 has a maximum limit of 2,147,483,647, and once that value was reached, the counter froze. Edition 2 supports INT64, which avoids this limitation.

 

The ION8650 meters with firmware v4.20 or later support Edition 2 (with the correct ICD file), so using the Edition 2 ICD or enabling rollover on the meter resolves the issue.

 

Mehran_Mehrnia_0-1768410154913.png

ION8650 sends very large Energy values over IEC 61850 Edition 2

IEC 61850 and ION technology - EN

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-01-14 09:04 AM . Last Modified: ‎2026-01-14 09:13 AM

0 Likes
1
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-14 09:04 AM

Hi @TJ22 

 

I believe this is related to IEC 61850 editions each meter's firmware and model supports.

 

The kWh delivery value stopped updating because the IEC 61850 configuration used Edition 1, where TotWh.actVal is defined as INT32. INT32 has a maximum limit of 2,147,483,647, and once that value was reached, the counter froze. Edition 2 supports INT64, which avoids this limitation.

 

The ION8650 meters with firmware v4.20 or later support Edition 2 (with the correct ICD file), so using the Edition 2 ICD or enabling rollover on the meter resolves the issue.

 

Mehran_Mehrnia_0-1768410154913.png

ION8650 sends very large Energy values over IEC 61850 Edition 2

IEC 61850 and ION technology - EN

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
TJ22
TJ22
Explorer

Posted: ‎2026-01-14 05:25 PM

0 Likes
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-14 05:25 PM

Hi Mehran,

 

Thank you for your explanation. This is very helpful information.

To enable the rollover function, can this be configured directly from the meter front panel, or does it need to be done using ION Setup software?

 

Best Regards,

Teja

Reply
TJ22
TJ22
Explorer

Posted: ‎2026-01-14 07:46 PM

0 Likes
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-14 07:46 PM

Hi @Mehran_Mehrnia 

 

I’ve checked that the energy rollover has been set to the maximum value from the beginning, but why did the counter freeze instead of rolling over to zero?

 

TJ22_0-1768448724618.png

 

Best Regards,

Teja

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-01-15 08:08 AM

1 Like
0
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-15 08:08 AM

Hi @TJ22 

 

Please note that when using rollovers above 10 million which is as default value as recommended by ION Setup, it will begin to lose significant digits especially when logging those energy readings.

Mehran_Mehrnia_0-1768492525625.png

 

If you choose to increase the rollover beyond default 10 million, the shown/recorded value will begin to lose precision somewhere above 16 million (where the register will seem to *freeze* for a period of time). Internally the meter is recording the value but what value is shown/recorded can not be properly represented since it is storing that value as a FLOAT32 which only have 7 to 8 digits of precision.

 

For example:

3,278,210,048(which is >>10million) might be shown accurately but the next available value that can be shown would be 3,278,210,304 so the reading will seem to *jump* at some point.

 

4F43 6584 in Float32 -> 3,278,210,048 in Decimal

Next Float32 is 4F43 6585 -> 3,278,210,304 in Decimal

3,278,210,304 – 3,278,210,048 = 256 kWh which means the larger the number becomes the bigger the gap.

https://www.h-schmidt.net/FloatConverter/IEEE754.html

 

Regarding your question, as explained previously, if the built CID file is based on Edition 1, it will be limited to INT32. Since the configured rollover value (10,000,000,000) exceeds the INT32 maximum of 4,294,967,296 (2^32), the meter continues logging large values internally, but when sending data via IEC 61850, it is constrained by the INT32 limit. As a result, the RTU stops updating because the value cannot increment beyond the maximum integer.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2026-01-15 11:30 AM . Last Modified: ‎2026-01-15 11:32 AM

0 Likes
0
441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-01-15 11:30 AM

Your problem is your using Edition 1 of 61850 which only supports INT32 shown here highlighted in green below:

Robert_Lee_0-1768505190076.png


The maximum value of INT32 has a range of -2147483648 to 2147483647 while UINT32 has a range of 0 to 4294967296.

Edition 2 of 61850 support INT64 which has a much larger range which is approx +/- 9.2 quintillion.


Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore