We’ve noticed that the load profile timestamps are offset by 8 hours from local time. We attempted to adjust the timezone settings, but the offset remains unchanged.
Could you please help investigate and resolve this issue?
Link copied. Please paste this link to share this article on your social media post.
If I am reading the documentation correctly, the ION meter will always output its data in UTC time, and the time zone offset is applied in the software (MV-90). If you absolutely must provide localtime, you could theoretically manually set the clock to the local time, but you will have to disable time sync, which is not recommended.
Link copied. Please paste this link to share this article on your social media post.
If I am reading the documentation correctly, the ION meter will always output its data in UTC time, and the time zone offset is applied in the software (MV-90). If you absolutely must provide localtime, you could theoretically manually set the clock to the local time, but you will have to disable time sync, which is not recommended.
Link copied. Please paste this link to share this article on your social media post.
Hello @Chen-Leo_Liang ,
Agree with Rob that likely UTC vs local time but would need more details to even begin looking at this.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
If you are using ION Setup to export HHF files it uses the published ITRON Generic HHF file format.
The HHF file indicates at byte 0xF4 with an ASCII character of 'U' to indicate that date/times are stored in UTC.