ION8650 Revunue meter Input Votage Reduce to 45V

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Pradip_SEL
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
3
263

ION8650 Revunue meter Input Votage Reduce to 45V

Dear All,

In one of our customer place(Power Plant) the meter measuring voltage reduce some time in a day around 45V(line to neutral).As per our ION8650 the measuring voltage specification

Input-voltage

characteristics (1)

Nominal voltage 57V to 277VLN rms

100V to 480VLL rms (35S)

Maximum voltage 347 VLN rms, 600 VLL rms (9S)

1)So in this case is it possible to measure the energy though ION8650 meter.

Tags (1)
3 Replies 3
Bojan
Captain Captain
Captain
0 Likes
2
235

Re: ION8650 Revunue meter Input Votage Reduce to 45V

Hi Pradip,

I think that the input-voltage specifications are limited by the operating range of the power supply if a non-auxiliary power supply is used.

So, if the meter is externally-powered as Auxiliary Low Voltage Supply [65-120 VLN RMS (+-15%)@47-63Hz 80-160VDC(+-20%)] or Auxiliary High Power Voltage Supply [160-277VLN RMS (+=20%)@47-63HZ 200-350VD(+-20%)], it is possible to measure the energy though ION8650 meter.

Best Regards,

Bojan

Pradip_SEL
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
1
235

Re: ION8650 Revunue meter Input Votage Reduce to 45V

Dear Bojan,

I will manage to power up meter by supply external High power supply voltage.So meter will be on.But the measuring input voltage some time 45V(Line to neutral) in a day.So that time whether our meter is capable to measure energy below nominal voltage is 57V LN.

Pls suggest me.

Bojan
Captain Captain
Captain
0 Likes
0
235

Re: ION8650 Revunue meter Input Votage Reduce to 45V

Hi Pradip,

My understanding is that the limitations, i.e. Standard 57-277 (+/-15%) VLN rms), are limited by the operating range of the power supply.

ION8600 Voltage Limitation.jpg

Best Regards,