Hello,
We are evaluating the retrieval of historical Load Profile / Revenue Log data from a PowerLogic ION8600 running firmware 8600V332 using Modbus.
We are referring to document 70022-0124-01, specifically Appendix B - Data Record / Modbus Map, which describes Data Recorder retrieval using registers 43001-43153.
We found Schneider FAQ FAQ000268832, which demonstrates this procedure on an ION8650. We also found the community discussions “Reading Revenue Log Data on ION 8650 via Modbus” and “Extract Data Recorder registers in PM8000/ION9000 with modbus protocol.”
From those references, we understand that Data Recorder retrieval through Modbus is supported on the ION8650, while PM8000/ION9000 do not support this mechanism.
We would therefore like to confirm specifically for the ION8600:
1. Does the Data Record / Modbus Map described in Appendix B (registers 43001-43153) support an ION8600 running firmware 8600V332?
2. The meter is configured with "Allow Modbus Programing = No". Does this setting prevent the control writes required by the retrieval procedure, specifically:
Our intention is only to retrieve existing historical records. We do not intend to modify the Data Recorder setup, framework, sources, logging interval, depth, or any other meter configuration.
From Appendix B, our understanding is that these writes are part of the Data Recorder selection/retrieval mechanism rather than changes to the Data Recorder setup. Could you please confirm whether this interpretation is correct for the ION8600?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hi @digowstm
1. Does the Data Record / Modbus Map described in Appendix B (registers 43001-43153) support an ION8600 running firmware 8600V332?
Firmware V330 or higher supports the procedures outlined Appendix B in the Modbus Map document.
2. The meter is configured with "Allow Modbus Programing = No". Does this setting prevent the control writes required by the retrieval procedure, specifically:
writing the Data Recorder Module Number to 43001;
writing the Starting Record to 43002-43003?
As I tested both conditions, with "Allow Modbus Programming" enabled and disabled, I was able to successfully write to and read from the Data Recorders via Modbus.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @digowstm
1. Does the Data Record / Modbus Map described in Appendix B (registers 43001-43153) support an ION8600 running firmware 8600V332?
Firmware V330 or higher supports the procedures outlined Appendix B in the Modbus Map document.
2. The meter is configured with "Allow Modbus Programing = No". Does this setting prevent the control writes required by the retrieval procedure, specifically:
writing the Data Recorder Module Number to 43001;
writing the Starting Record to 43002-43003?
As I tested both conditions, with "Allow Modbus Programming" enabled and disabled, I was able to successfully write to and read from the Data Recorders via Modbus.
Best Regards,
-Mehran
L3 Expert Advanced metering