ION7650, Waveform recording by external trigger (Digital Input)

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa205726_brid
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
1
224

ION7650, Waveform recording by external trigger (Digital Input)

Hi Robert Lee​,

I need help about ION7650: I need to set the device to capture a waveform on external trigger, for example, with trigger on digital input. Also, I wish to set the the depth, format and delay cycles.

Do you know how to do with ION Setup?

Thanks.

Regards 

1 Reply 1
Yut
Captain
Captain
0 Likes
0
190

Re: ION7650, Waveform recording by external trigger (Digital Input)

To set format and delay cycle set the Sag/Swell and Transient module.

To set the depth set the waveform recorder module.

To add trigger from external digital input look at the Pulse Merge module name Wfm Tg Mg-Sg/Sw and Wfm Tg Mg-Trnst

there are empty inputs you can add trigger into them. Note that pulse from digital input will be 1 cycle delay.

See ION Reference for detail operation.