Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7400 vs PM8240

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7400 vs PM8240
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
she
she
Explorer

Posted: ‎2026-10-23 06:40 PM

0 Likes
2
224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-23 06:40 PM

ION7400 vs PM8240

Questions on ION7400 and PM8240.
1. What is the differences and similarity between PM8240 and ION7400?
2. Which model (ion7400 or pm8240) is suitable /recommended to be used in One-Phase Traction Transformer for Railway Application?
3. Info: The connection of Voltage is via Voltage Transformer - VT secondary of 110V (132000/110V L-N), Connection of Current is via Current Transformer of 900/1A.
4. Does ION7400 able to show accurate One Phase Voltage, Current, Power quantities (W, Var, VA), PF based on VT connection of L-N?
5. If yes, we would appreciate support on how the configuration work for single phase Voltage, Current and Power.
6. For One-Phase Railway Application, Power Quality analysis of Harmonic Distortion, will the meter able to provide accurate analysis based on one-phase connection?

Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-10-26 08:10 AM . Last Modified: ‎2026-10-26 08:15 AM

1 Like
0
210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-26 08:10 AM

Hi @she 

 

1- PM8240 and ION7400 are technically closely related ION-based advanced meters and share many metering, power quality, logging, alarming, communications, and ION programmability capabilities.

The primary difference is their market and application positioning. The ION7400 is specifically positioned as an advanced utility meter for transmission and distribution applications, including substation feeder metering, revenue metering, extensive power-quality monitoring, end-feeder monitoring, and digital fault recording.

Therefore, while both meters offer similar advanced metering and PQ capabilities, ION7400 is the specifically positioned product for utility, transmission/distribution, substation, and revenue-metering applications, whereas PM8240(Standard feature set) is part of the PM8000 advanced power and energy metering family.

 

2- Both PM8240 and ION7400 support single-phase metering. However, for this railway traction transformer/substation application, ION7400 would generally be the recommended choice, particularly for utility, transmission/distribution, and substation environments. Schneider Electric positions ION7400 as an advanced utility meter with capabilities including advanced PQ monitoring, revenue metering, digital fault recording, Transformer/Line Loss Compensation, and Instrument Transformer Correction. ION7400 also offers utility-oriented capabilities such as flicker measurement, whereas the PM8240 with Standard feature set has more limited PQ functionality.


One important consideration is the traction-system frequency. The ION meters specified-accuracy frequency range is 42 to 69 Hz (50/60 Hz nominal).

Note: The final meter selection should be confirmed with the local Schneider Electric Front Office to ensure compliance with the applicable project specifications, local standards, utility requirements, and railway-specific requirements.

 

4- Yes. Both meters support single-phase measurements and can accurately measure/calculate Active Power (W), Reactive Power (var), Apparent Power (VA), Power Factor (PF), phase-to-neutral voltage (Va), and line current (Ia) using a single phase-to-neutral VT input (110 V) and the corresponding CT input (1 A), provided the meters are correctly configured and operated within their specified measurement ranges.

 

5- For a single-phase L-N application, configure the meter Volts Mode as SINGLE and connect the voltage signal to V1 and Vref/VN, with the corresponding current connected to I1. Configure the VT ratio as 132000/110 V and CT ratio as 900/1 A.

After configuration, verify voltage, current, power, power factor, and phasor orientation against the actual system. For power-quality functions such as Sag/Swell, the default ION framework may also require adjustment of unused voltage inputs for proper single-phase operation. For more info, please check this forum.

 

6- The meter can provide power quality and harmonic analysis on the measured single-phase voltage and current inputs.

Harmonic Distortion: The meter can calculate individual voltage and current harmonics, as well as harmonic distortion measurements, for the connected phase.
Waveform Capture and Sags/Swells: The meter supports waveform recording and voltage disturbance monitoring. For a single-phase application, the associated PQ modules and settings should be reviewed to ensure they are configured appropriately for the connected voltage and current channels.
Single-Phase Application: Harmonic analysis can be performed on the connected single-phase voltage and current signals. 

Therefore, the ION7400 can be used to analyze the voltage and current harmonic distortion of this single-phase traction-transformer measurement, subject to the meter's specified operating/accuracy range and the accuracy and frequency response of the connected VT and CT.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-11-04 07:57 AM

0 Likes
0
106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-11-04 07:57 AM

Hello @she ,

 

Did the reply from Mehran help answer your questions?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore