Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION6200RMD

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION6200RMD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
hjain
hjain
Explorer

Posted: ‎2026-05-14 08:30 AM

0 Likes
1
360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-14 08:30 AM

ION6200RMD

I have seven ION6200RMD, they are daisy chained using RS485 Modbus protocol to a PM 8500, I used to be able to read all 6200 using PM 8500 as the gateway until I had to replace the PM8500, since the replacement I have not been able to receive data from ION 6200 while I can see the PM 8500 data. PM 8500 is used as a gateway using IP and Modbus RTU setup and each ION as Modbus RTU device. I have checked all com ports setting and they all seem to be okay. I tried connecting 485 wires to a different 485 Modbus compatible device but was not successful in seeing any data from ION 6200. I have also reset the 6200 but still unable to see the data. Anyone has any recommendation as how I should trouble shoot it. 

Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-05-19 07:47 AM

0 Likes
0
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-19 07:47 AM

Hello @hjain ,

 

I would start with a known good RS-485 converter that can work on a laptop, example RS-485 to USB.

1) Disconnect one ION6200 meter and connect to the converter.

2) Run a modbus client that can use the converter to send modbus connected to the meter.

3) Confirm that meter is able to respond to modbus. If not, will need to troubleshoot with the single meter and directly connected. Could be DeviceID, protocol on meter, baud rate etc. Hard to give exact recommendations over a forum.

4) Once you have 1 meter working correctly, attach a second meter. Confirm that you can talk to both meters. If no communication will need to troubleshoot. Trying to isolate where the problem could be, perhaps try a different meter. If one meter is behaving badly it could affect all meters on the line.

5) Repeat adding meters one at a time to try and isolate where issue lies.

6) Once you have confirmed that all ION6200 meters are working, connect back to the ION8500 meter.

 

Note that ION8500 meters and ION6200 meters have been obsolete for a while now. There is limited tehcnical support available for these meters.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Reply 1
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-05-19 07:47 AM

0 Likes
0
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-05-19 07:47 AM

Hello @hjain ,

 

I would start with a known good RS-485 converter that can work on a laptop, example RS-485 to USB.

1) Disconnect one ION6200 meter and connect to the converter.

2) Run a modbus client that can use the converter to send modbus connected to the meter.

3) Confirm that meter is able to respond to modbus. If not, will need to troubleshoot with the single meter and directly connected. Could be DeviceID, protocol on meter, baud rate etc. Hard to give exact recommendations over a forum.

4) Once you have 1 meter working correctly, attach a second meter. Confirm that you can talk to both meters. If no communication will need to troubleshoot. Trying to isolate where the problem could be, perhaps try a different meter. If one meter is behaving badly it could affect all meters on the line.

5) Repeat adding meters one at a time to try and isolate where issue lies.

6) Once you have confirmed that all ION6200 meters are working, connect back to the ION8500 meter.

 

Note that ION8500 meters and ION6200 meters have been obsolete for a while now. There is limited tehcnical support available for these meters.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore