Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION Setup errors

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION Setup errors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa99134
sesa99134 Leader
Leader

Posted: ‎2015-09-15 05:33 PM . Last Modified: ‎2020-04-22 01:29 AM

0 Likes
3
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-15 05:33 PM

ION Setup errors

Hello Robert Lee,

 

I think you are able to help me in this case.

Most of the time I'm getting this error trying to paste a DCF file in a meter (ION8XXX series), after to select the dcf file and to initiate dcf pasting this message is shown:

Captura de pantalla 2015-09-15 a la(s) 19.26.14.png

Any idea what is happening here?. I've updated to the last ION Setup version and the error persist.

 

Thanks!.

 

Adelmo

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-09-16 08:56 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-16 08:56 AM

Hi there,

From the look of the exception, it seems ION Setup is attempting to write to a file (likely the TEMPLATE.LOG file) but is unable to do so for some reason.  Check that the Windows user you have logged on with has full read/write permissions for the ION Setup Config folder (this is typically C:\ProgramData\Schneider Electric\ION Setup but you can view the location from Tools -> Options).

You could also email me (Robert.lee@schneider-electric.com) the DCF file you are pasting and I can look into if there is something that isn't working correctly (you could also send me your TEMPLATE.LOG file if it isn't the cause of the file I/O error).

See Answer In Context

Reply
Replies 3
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-09-16 08:56 AM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-16 08:56 AM

Hi there,

From the look of the exception, it seems ION Setup is attempting to write to a file (likely the TEMPLATE.LOG file) but is unable to do so for some reason.  Check that the Windows user you have logged on with has full read/write permissions for the ION Setup Config folder (this is typically C:\ProgramData\Schneider Electric\ION Setup but you can view the location from Tools -> Options).

You could also email me (Robert.lee@schneider-electric.com) the DCF file you are pasting and I can look into if there is something that isn't working correctly (you could also send me your TEMPLATE.LOG file if it isn't the cause of the file I/O error).

Reply
sesa99134
sesa99134 Leader
Leader

Posted: ‎2015-09-17 07:48 AM

0 Likes
1
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-17 07:48 AM

Hi Robert Lee,

Thanks you were right, running as administrator everything is ok!!!.

Adelmo

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-09-17 09:00 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-17 09:00 AM

The final solution then is to use the Administrator account and grant appropriate access control to the user(s) you wish to allow access to that folder.  Use Windows Explorer, open up the folder properties and click on the Security tab.  Add permissions for the user (or group if you wish to have a set of users) and grant them full control.

Here is what it should like after I've added the "Users" group to have the needed access.

security2.png

The latest installer should do this automatically but if you upgrading from an older version, since the folder already exists, the appropriate rights/access might not be assigned properly.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore