That could not be fixed until a manual update of Frequency Groups' setup register (a real change of setup register value and send to meter).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @eRicC ,
I know that this was also a case with Technical support. Will confirm details through the case and update here if there is specific information that can be shared.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @eRicC ,
Regarding point 1, there could be a work around but does require a few additional modules to achieve. Ideal would be to have a frequency group that is a large range however I believe you are using all 50 groups in your configuration. Will need to select a frequency group that has as large a range as possible or known to have a changing value.
Will need a new periodic timer module that is set to 1/2 cycle. Will need a new differentiator module, the trigger input is linked to the new periodic timer module, the source is linked SSO frequency group. This way the differentiator module will be 0 most of the time then for 1 half cycle have a non zero value. The output from the differentiator will need to be linked to a convert module. Link the On pulse of convert module to the input of the data recorder module.
Regarding point 2, will need to confirm with the team. All I know for sure is that the aggregation is for all peaks that exceed the threshold that fall within the defined frequency group.
regarding point 3, the assumption has been than once configured, user would not want to disable the module.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Update for Point 2, the frequency group is aggregating all the spectral content within the defined frequency range not peaks.
Link copied. Please paste this link to share this article on your social media post.
Thanks for the workaround.
Would the use of differentiator module fall in a scenario when two or more consecutive Change of Value events happen such that failed to let convert module to reset or resend the trigger pulse given the output would be stayed in non-zero value.
Would it sound more robust to have a store module (linking to the same periodic timer module) recording the same Frequency Group magnitude as "Previous Records" and followed by using Relative Setpoint Module to compare the change of New and Previous Records then send a trigger pulse / convert module. (That logic would sound like the feature in Arithmetic Module (but that only for non-HS) to compare previous records).
Happy to discuss.
Link copied. Please paste this link to share this article on your social media post.
Hello @eRicC ,
I am not sure how your solution would be more robust than what I suggested. The SSO module is a little different than all other ION modules in that the output is approximately once a second but not running within the one second task like other modules.
Differentiator module would be running high speed so module would be 0 until there is a change at the output of SSO.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Thanks and do understand the benefit of using Differentiator module which could reduce the use of modules compare to my solution.
From the recent test I would suggest a fine tuning of linking that to the Peak1 Frequency / Magnitude instead of a Frequency Group because a new bug is found - all Frequency Groups would return NULL value (n/a) after power cycling the meter.
And that could not be fixed until a manual update of Frequency Groups' setup register (a real change of setup register value and send to meter).
I have tested twice and confirmed this behaviour.
With all the bugs identified, there is a necessary of releasing a firmware update.
Link copied. Please paste this link to share this article on your social media post.
Hello @eRicC ,
I have reported this new behavior to the firmware team. When I have an update to provide I will update this post.
Regards,
Charles